    Can I put to PHPM-PA-120-WH on to a RRD-10D dimmer?

    Can I put two PHPM-PA-120-WH on to a RRD-10D dimmer?

    On this link:http://www.lutron.com/TechnicalDocum...ry/369-356.pdf

    It says Up to 3 power modules may be wired on a single GRAFIK Eye zone. So I am hoping this is the same for a in wall dimmer as well like the RRD-10D dimmer.

    And will each PHPM-PA-120-WH add 1920 watts to what the dimmer can handle? Would one use a 6d or 10d or does it matter? It sounds like the PHPM determines the load so a 6d would be fine.

    I need 2400 watts on a single dimmer for incandescent loads.

    Thank you in advance for your help!

  2. #2
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    RA2-Designer-Gal,
    Specs for the PHPM modules require a neutral wire dimmer to control the PHPM. The 10D will not work. Tech support might be able to help and see if the 6CL might be the answer.
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

  3. Thanks RA2-Designer-Gal thanked for this post
  4. #3
    Authorized Lutron Contributor
    Join Date
    Apr 2013
    Posts
    403
    The PHPM-PA interface needs a neutral wire control so the RRD-10ND dimmer would be the proper dimmer to use. You can control up to 3 interfaces from the same dimmer.

  5. Thanks RA2-Designer-Gal thanked for this post
  6. #4

    Exclamation Help needed! 1000 Watts LEDs on RRD-10ND - do I need a PHPM-PA?

    Help needed!

    So this client has decided to go LEDs due to the high wattage Incandescent issue.

    So we spec'd out an LED candelabra bulb that will work at 25 Watts and is listed to work with the10ND.

    However, I am uncertain that the 1000 watts of LEDs will work on the 10ND. The new bulbs comes out to be exact 1000 watts -
    8 bulbs per fixturex25 watts=200 200 watts x 5 fixtures=1,000 watts

    And I seem to recall that the LEDs draw a lot more power when ramping on. My instincts are telling me to add in the PHPM-PA anyways due to the ramp on issue.

    However, it seems towork fine in the RA2 software - no caution signs pop up.

    And the electrician has agreed to install the 10ND in its own box so no deganging issues there.

    But I still have a nagging feeling the PHPM-PA is still needed.


    Thank you in advanace - I so appreciate your feedback & suggestions!

  7. #5
    Ughhhh! Blond moments are so embarassing. LED bulbs are 4 watts not 25 watts so I should be fine.

    Thank you so very much for your help!

  8. #6
    Junior Member
    Join Date
    Feb 2017
    Posts
    1

    PHPM-PA for LED lights

    Hi! I wanted to ask you if you know if the PHPM-PA can dim LED lights? The Lutron dimming system is a Grafik Eye GRX 3506.

    Thank you!!



    Quote Originally Posted by RA2-Designer-Gal View Post
    Help needed!

    So this client has decided to go LEDs due to the high wattage Incandescent issue.

    So we spec'd out an LED candelabra bulb that will work at 25 Watts and is listed to work with the10ND.

    However, I am uncertain that the 1000 watts of LEDs will work on the 10ND. The new bulbs comes out to be exact 1000 watts -
    8 bulbs per fixturex25 watts=200 200 watts x 5 fixtures=1,000 watts

    And I seem to recall that the LEDs draw a lot more power when ramping on. My instincts are telling me to add in the PHPM-PA anyways due to the ramp on issue.

    However, it seems towork fine in the RA2 software - no caution signs pop up.

    And the electrician has agreed to install the 10ND in its own box so no deganging issues there.

    But I still have a nagging feeling the PHPM-PA is still needed.


    Thank you in advanace - I so appreciate your feedback & suggestions!

  9. #7
    Senior Member
    Join Date
    May 2013
    Posts
    420
    Hello benjacruzg,
    I would need to refer you to our resources for checking if the LED you have is tested by Lutron. Please visit this web page for further assistance. www.lutron.com/led

Similar Threads

  1. Link wall dimmer to plug dimmer
    By Jwindle in forum Programming - CAS
    Replies: 14
    Last Post: 06-16-2017, 04:08 PM
  2. How does a CL dimmer differ from a Standard Dimmer?
    By BrianWren in forum General Discussion - LED
    Replies: 4
    Last Post: 04-30-2014, 03:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •