Is it possible? Should be simple but I do not see the option in QS, maybe I am missing it. To clarify, I am asking if at the load level I can define "on/off only" effectively making it function as if it were connected to a relay module.
Thanks
Is it possible? Should be simple but I do not see the option in QS, maybe I am missing it. To clarify, I am asking if at the load level I can define "on/off only" effectively making it function as if it were connected to a relay module.
Thanks
We would recommend you go to the "Design->Loads" screen and ensure the "Load Type" column is visible. If not, please click on the "Customize Columns" link and check the "Load Type" column. If you select a load type that is "Switched" or "Relay", the only options you will see when you are programming these loads will be "On, Off, and Unaffected".
Perfect Armando, I had missed the "edit fixture" area which allows me to edit the value of that column, I was trying to edit a load after the fact to make it non-dimmable. Thanks!