Thread: Momentary / maintained outputs on QSE-IO

  1. #1
    Junior Member
    Join Date
    Sep 2014
    Posts
    7

    Momentary / maintained outputs on QSE-IO

    I'm trying to control a low voltage dimmer via a QSE-IO output, this particular device has to wires that take a momentary contact closure input.
    One press will turn it on, press it again and it turns off but if the device is on and you hold the contacts closed, it will dim the lights down and then up until the button is released. Is there any way this could be accomplished with a QSE-IO?
    Any suggestion?

  2. #2
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    513
    You can make the CCO output maintained. On the keypad button, program it as a dual action. On the press, close the CCO, on the release, open the CCO. As long as you have the button pressed, the CCO will be closed; as soon as you release it, the CCO will open.

Similar Threads

  1. Assign Inputs/Outputs Pop-up Missing or Disappeared
    By Ty W. in forum Troubleshooting - HWQS
    Replies: 1
    Last Post: 05-11-2017, 01:50 PM
  2. VCRX - Integration IDs for Outputs
    By DSinSF in forum General Discussion - HWQS
    Replies: 2
    Last Post: 11-03-2014, 03:31 PM
  3. Momentary button like Raise & Lower...
    By whdigital in forum Programming - HWQS
    Replies: 1
    Last Post: 10-20-2014, 02:06 PM
  4. Open outputs on Lutron QS dimmers and relay modules
    By etienneterblanche in forum General Discussion - HWQS
    Replies: 2
    Last Post: 08-26-2014, 02:10 PM
  5. Can I use an 8-ANS to simulate a momentary contact
    By DSinSF in forum General Discussion - HWQS
    Replies: 3
    Last Post: 10-14-2013, 01:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •