    What type of sensors can be connected to inputs of QSE-IO module?
    Is it possible to connect 230Vac sensor?

    Is it possible to connect any of down listed sensors to IO input:

    1)Steinel IR Quattro 000349
    2)Steinel IR Quattro COM2
    3)Steinel IS 345WE 606510

    Please comment.

  2. #2
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    513
    You can have sensor connections to the contact closure inputs of the QSE-IO that meet the specifications below. Since the QSE-IO does not see the input voltage to the sensor and deals only with low voltage, the 230V may not be part of the equation.

    Five Input Terminals:
    • Accept maintained inputs and momentary inputs with
    40 msec minimum pulse times.
    • Of f-state leakage current must be less than 100 ľA.
    • Open circuit voltage: 24 V
    maximum.
    • Inputs must be dry contact closure, solid state, open
    collector, or active-low (NPN)/active high (PNP) output.
    - Open collector NPN or active-low on-state voltage
    must be less than 2 V
    and sink 3.0 mA.
    - Open collector PNP or active-high on-state voltage
    must be greater than 12 V
    and source 3.0 mA

Similar Threads

  1. Occupancy/vacancy sensors
    By Ekkoville in forum General Discussion - CAS
    Replies: 5
    Last Post: 04-14-2016, 01:46 PM
  2. Dual Occupancy Sensors
    By schalliol in forum General Discussion - RA2
    Replies: 4
    Last Post: 09-30-2014, 08:34 AM
  3. maestro occupancy sensor
    By Christiann in forum General Discussion - Controls
    Replies: 0
    Last Post: 07-05-2014, 04:14 PM
  4. Pico and Occ Sensors out of programming
    By mandbelectric in forum Troubleshooting - RA2
    Replies: 1
    Last Post: 12-31-2013, 03:11 PM
  5. Motion sensor Overide
    By mdfeather in forum Programming - RA2
    Replies: 2
    Last Post: 11-17-2013, 07:37 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •