    0-10V wiring with an RPM

    I am working on a project and we do not have space in our PNL-8 for a TVM Kit so we were thinking of going with the LMJ-5T-DV-B. I just want to make sure I get this right for wiring. Would I come out of my RPM-4A to the line side of the RF dimming module then from load side I go to fixture and also bring the 0-10V wire to fixture?
    Thanks for any help

  2. #2
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    289
    cabethesda, the LMJ-5T-DV-B would not get wired to the output of a RPM. The unit would get a constant hot to the black wire, switched hot to the red wire and a neutral to the white. The low voltage 0-10v wires would then get plugged into the front of the LMJ-5T-DV-B and run to the ballast or driver of hte fixture.

  3. Likes Armando B. liked this post

Similar Threads

  1. Keypad wiring redundancy
    By Ty W. in forum Best Practices - HWQS
    Replies: 12
    Last Post: 04-22-2018, 11:06 PM
  2. Wiring Hybrid Repeaters
    By Armando B. in forum Design Assistance - HWQS
    Replies: 0
    Last Post: 04-18-2014, 04:46 PM
  3. HWQS Honeywell wiring
    By Ken C. in forum General Discussion - HWQS
    Replies: 3
    Last Post: 04-04-2014, 05:30 AM
  4. Network wiring QSGRJ-4P to QSE-CI-NWK-E
    By Marcoscab in forum Design Assistance - HWQS
    Replies: 1
    Last Post: 11-01-2013, 02:27 PM
  5. QS & shade wiring
    By Tony Sena in forum Best Practices - HWQS
    Replies: 1
    Last Post: 06-26-2013, 06:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •