Thread: Extent of alarm.com integration

  1. #1

    Extent of alarm.com integration

    Is the integration with alarm.com security systems limited to just triggering scenes when an alarm happens?
    Or would it be possible for scenarios where an alarm.com motion sensor could be used to act as an occupancy sensor and trigger a scene? Conversely, could a RadioRA2 occupancy sensor become an input to the security system panel?
    This would be beneficial in the following ways
    1. Reducing the number of sensor warts on either the ceiling or walls
    2. The Simon XT panel has a hard limit of 40 RF devices. It is conceivable that the limit could be reached if a home owner decides to put sensors on all exterior doors, windows, interior environment, glass break & motion sensors, ...

  2. #2
    Authorized Lutron Contributor
    Join Date
    Apr 2013
    Posts
    403
    You can use alarm system triggers (motion sensors, door sensor, etc.) to trigger actions in the RadioRA 2 system. Please be aware that these messages take the following path and thus could result in undesirable delay: sensor sends message to panel, panel sends message to Alarm.com servers over the cellular network, the Alarm.com servers send messages via the internet to the RA2 main repeater to trigger actions


    Unfortunately this is not possible to have the RadioRA2 occupancy sensors become an input to the security system panel. Alarm.com would have to add this feature to their service.

  3. #3
    Thanks.
    Would there be a way to wire the HW outputs from the Simon XT panel into the master repeater? Or is the alarm.com route the only way?

  4. #4
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    402
    Quote Originally Posted by Bktay View Post
    Thanks.
    Would there be a way to wire the HW outputs from the Simon XT panel into the master repeater? Or is the alarm.com route the only way?
    The Main Repeater does not have any contact closure inputs on it. The only device on a RadioRA 2 system with contact closure inputs is the Visor Control Receiver. If the Simon XT panel can send a dry contact closure to the Visor Control Receiver then it can activate scenes.

  5. Thanks Bktay thanked for this post
  6. #5
    With the system setup with a static IP and the gateway correctly configured, the M status light still continues to blink once every 4 seconds. FrontpointSecurity (an Alarm.com provider) cannot add the main repeater as there is an error message stating that the main repeater has not communicated yet...

    What ports need to be open in the firewall for the alarm.com integration to work?
    Thanks

  7. #6
    Resolved. The gateway address was not set correctly (?system,13 via telnet showed 0.0.0.0) although it showed up in the RadioRA2 Essentials software.

    Solution - set the gateway address