Thread: HWQS Honeywell wiring

  1. #1
    Junior Member
    Join Date
    Feb 2014
    Posts
    3

    HWQS Honeywell wiring

    I am replacing a Honeywell 4-wire stat with a LR-HWLV-HVAC. The new stat requires a common on terminal "C", is this not the same as as the common ground with-in the furnace? I do have a spare wire running from the furnace to the thermostat, I just want to be sure before I connect the common. Honeywell tech support was "USELESS".

  2. Thanks digit1 thanked for this post
  3. #2
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    513
    You should have a common "C" on the HVAC system itself; if you have an additional wire, this could connect the common terminal from the HVAC system to the TouchPro "C" terminal. Please see pages three and four on the attached wiring document as it goes over the different wiring configurations for the type of HVAC systems. It will highlight was is needed in the "C" terminal for the HVAC system you have.
    Attached Files Attached Files

  4. #3
    Junior Member
    Join Date
    Feb 2014
    Posts
    3
    Thanks for the help that is what I thought

  5. #4
    It was pretty hard to do. I just let my brother do change the wiring for me. He is an expert with that.

Similar Threads

  1. Keypad wiring redundancy
    By Ty W. in forum Best Practices - HWQS
    Replies: 12
    Last Post: 04-22-2018, 11:06 PM
  2. Network wiring QSGRJ-4P to QSE-CI-NWK-E
    By Marcoscab in forum Design Assistance - HWQS
    Replies: 1
    Last Post: 11-01-2013, 02:27 PM
  3. QS & shade wiring
    By Tony Sena in forum Best Practices - HWQS
    Replies: 1
    Last Post: 06-26-2013, 06:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •