Thread: HRD Dimmer serial addressing problem

  1. #1
    Junior Member
    Join Date
    Apr 2017
    Posts
    2

    HRD Dimmer serial addressing problem

    Hello all. Hoping someone might be able to help me out with a dimmer addressing issue. I recently added an HRP5-120 RF processor to my existing Illumination system. Have gotten everything setup and working except for some used HRD-6's & 5NE's that I picked up. They refuse to show up upon triple-tap in serial address mode. Have several new keypads and HRD's that came up with no problem, so this leads me to think that there is an RF reset procedure I'm not aware of?

    I have tried the APM reset procedure (Switch FASS on while holding tap button until load dims twice). Have also found reference to a reset by triple-tap/hold, triple-tap again procedure but the dimmers do not respond to this with scrolling LED's.

    Any suggestions would be appreciated!!

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    You are correct. If the device is registered to another system you must reset it prior to adding to a new system. The triple tap reset only works on QS systems (RR2, HQS). It's been a while since I have done this but...

    Pull the gap switch.
    Press and hold the paddle and up rocker (dimmer only)
    Push the gap switch in - dimmer LEDs will cycle, switch LED will blink
    Release and press and hold the paddle and down rocker (dimmer only)
    Release when LED flashes
    It takes 10-15 seconds to complete the reset.

    FYI - if you go to lutron.com, service & support, legacy devices there is some documentation for your system.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  3. Thanks Blair S. thanked for this post
  4. #3
    Junior Member
    Join Date
    Apr 2017
    Posts
    2

    Solved!!

    That did it! Thanks so much Randy.

  5. Likes randyc, Blair S. liked this post

Similar Threads

  1. Problem while adding dimmer via App.
    By pandyarajen in forum Troubleshooting - CAS
    Replies: 3
    Last Post: 08-01-2016, 04:31 PM
  2. Problem with dimmer
    By DougS in forum Troubleshooting - RA2
    Replies: 1
    Last Post: 05-09-2016, 01:14 PM
  3. Problem with Serial Number Addressing and Keypads
    By scholl_r in forum Troubleshooting - Legacy HW
    Replies: 7
    Last Post: 03-08-2016, 01:06 PM
  4. Addressing Shades that were Previously in Another System
    By Armando B. in forum Design Assistance - RA2
    Replies: 1
    Last Post: 03-13-2014, 03:10 PM
  5. TVM2 addressing
    By totesthouse in forum Design Assistance - HWQS
    Replies: 3
    Last Post: 01-15-2014, 08:49 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •