Here's my setup:
One GRX-3504, A1
Two wallstations, addresses 1 and 2
One GRX-AV
One LOS-CDT-200-WH connected to this GRX-AV, with the intent of serving as an occupancy sensor.
I have put the OS in 8-second test mode and connected it to Common-1 on the inputs of the GRX-AV. I have also gotten the GRX-3504 to "listen" to the GRX-AV on input 1 only (the only input I'm using). I have set the DIP switches to OS1 mode.
If I stay put for 8 seconds, the lights stay on. If I pull the "1" input wire, the lights still stay on. Am I missing something?
Thanks!