Thread: Help: How to install 2 PD-6WCL in a dual switch gangbox?

  1. #1
    Junior Member
    Join Date
    Feb 2018
    Posts
    2

    Help: How to install 2 PD-6WCL in a dual switch gangbox?

    Hi folks...need some help in installing two PD-6WCL (no neutral wire) in the same gangbox.


    One switch will control one side of the basement's lights and the other switch will control the other side. Both of them are connected to a single 15 amp circuit.


    The gangbox has 9 cables coming out of it:

    WHITE: 3 neutral (all tied together)
    BARE COPPER: 3 ground (each tied to a different screw on the gangbox)
    BLACK: 1 hot (going to the circuit breaker) and 2 toggles (each going to one side of the room lights)

    The Caseta dimmer switch has 3 wires each (1 ground and 2 black...so 6 in total for both the switches). How should I be wiring the 4 black wires to the 3 black wires coming out of the gangbox?

    Appreciate the help! Thanks...

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,605
    All of the grounds should be connected together, along with the metal box and the ground wires from the dimmers.

    The hot wire will be connected to both dimmers. One of the toggles (switch leg) will be connected to each dimmer.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  3. #3
    Junior Member
    Join Date
    Feb 2018
    Posts
    2
    Quote Originally Posted by randyc View Post
    All of the grounds should be connected together, along with the metal box and the ground wires from the dimmers.

    The hot wire will be connected to both dimmers. One of the toggles (switch leg) will be connected to each dimmer.
    Thanks randyc! Does it matter which of the 2 black wires (in the switch) I connect to the hot wire?

  4. #4
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,605
    No. If the switch/dimmer is polarity sensitive it will have a black wire/terminal for power in and a different color for power out.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

Similar Threads

  1. Replies: 4
    Last Post: 09-07-2017, 09:46 PM
  2. Dimmer Switch install in bathroom.
    By Fastermac in forum General Discussion - CAS
    Replies: 3
    Last Post: 08-12-2017, 08:10 AM
  3. Pd-6wcl - no power at switch - lights working
    By Sonianic in forum Troubleshooting - CAS
    Replies: 2
    Last Post: 04-14-2017, 01:22 PM
  4. Dual 0-10V inputs on a fixture
    By Craig W. in forum Design Assistance - HWQS
    Replies: 1
    Last Post: 08-04-2015, 09:08 PM
  5. Dual Occupancy Sensors
    By schalliol in forum General Discussion - RA2
    Replies: 4
    Last Post: 09-30-2014, 08:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •