Had a call out from an old client that's had an install for about 4 years now. There's a problem with the ground floor switches and circuits, randomly not working.
The ground floor is on Link 2 and only link 2 has the issue.
However, if I remove link 1 from the processor then link 2 behaves correctly. Also have a "QS device not in database : Link 2 address 35. I have 34 devices assigned in link 2.
I have re activated all the devices throughout program, all 94 of them and even swapped out the processor but no avail. I have disconnected whole sections of the link circuits but its utterly random and can't pin down an individual device that's causing the Link 2 to crash.
Any ideas.