    PD-6ANS Not turning LEDs all the way off...

    Moved a PD-6ANS from one room to another. Same LEDs in both rooms. Old room worked fine. New room the lights turn almost all the way off but there's still a hint of light coming from them. I know on the dimmers you can adjust the low end trim to fix this, but on this on/off switch is there any way to fix this?

    Thanks!

  2. #2
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    635
    Get a LUT-MLC (Minimum Load Capacitor) and wire it in addition to the loads.
    http://www.lutron.com/TechnicalDocum...94_LUT-MLC.pdf

  3. Thanks SDR-Mike thanked for this post
    Likes SDR-Mike liked this post
  4. #3
    Junior Member
    Join Date
    Oct 2016
    Posts
    18
    Quote Originally Posted by Brian W. View Post
    Get a LUT-MLC (Minimum Load Capacitor) and wire it in addition to the loads.
    http://www.lutron.com/TechnicalDocum...94_LUT-MLC.pdf
    The link shows that this is used for switches without a neutral? My neutral wire is hooked up. SO do I not use the neutral wire in my junction box then?


    And 2 questions...

    1. Why would it work on the exact same set of lights in the next room over without needing this?

    2. Why is this MLC ALWAYS the answer? If so many people have issues that this solves, why is this not built in or come with a switch. Now Lutron switches cost $60-$100 if you factor in buying this with every switch purchase.

    I'm not trying to be rude/mean, I'm just honestly asking.

  5. #4
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    635
    Still use the neutral on the PD-6ANS. Just use this in addition to the switch.

    1. With unknown or untested LEDs, it could be multiple factors. I've had many cases where it's been: "it works fine with 3 of these LEDs, but it's not working correctly with 6 of the same LEDs (or vice versa)".

    2. It's our best guess at it working. With the huge variety of LEDs being manufactured nowadays, we don't have the manpower to test them all. The PD-6ANS switch always works fine with incandescent or halogen bulbs. With the way digital dimmers/switches work, there can still be a very small amount of voltage on the output of the switch, even when the switch is off, to keep the microchip running. Incandescent or halogen bulbs aren't affected by this small voltage, but some LEDs are sensitive enough to pick up on this voltage and stay lit at a very dim level. The LUT-MLC helps with this small voltage.

  6. Thanks SDR-Mike, randyc thanked for this post
    Likes SDR-Mike liked this post
  7. #5
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    The MLC isn't always the answer. It is the miracle device that does fix a lot of issues though. Lutron does include the MLC with a couple of models. I'm sure there is a detailed (i.e. boring) explanation of why some models and not others. I'm sure is evaluating incorporating the MLC into the dimmer design. They also have to determine where adding the MLC might have a negative effect.

    The other issue I have seen is from a shared neutral. We used to see this a lot with CFLs and other fluorescents. It is why a dimmer sometimes works in one room and not in the next. The MLC won't fix a shared neutral.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  8. #6
    Junior Member
    Join Date
    Oct 2016
    Posts
    18
    Quote Originally Posted by Brian W. View Post
    Still use the neutral on the PD-6ANS. Just use this in addition to the switch.
    So can you dumb down the instructions for me and show/tell me exactly how to wire it in with a neutral switch?

    Thanks for your help with this

  9. #7
    Junior Member
    Join Date
    Oct 2016
    Posts
    18
    Quote Originally Posted by NathanJax View Post
    So can you dumb down the instructions for me and show/tell me exactly how to wire it in with a neutral switch?

    Thanks for your help with this
    bump.........

  10. #8
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    The MLC wires in parallel to the load. Connect one lead to the dimmer/switch output and the other to the neutral.

    http://www.lutron.com/TechnicalDocum...ary/041294.pdf
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  11. #9

    23V between load and neutral when off ?!?

    Quote Originally Posted by Brian W. View Post
    Still use the neutral on the PD-6ANS. Just use this in addition to the switch.

    1. With unknown or untested LEDs, it could be multiple factors. I've had many cases where it's been: "it works fine with 3 of these LEDs, but it's not working correctly with 6 of the same LEDs (or vice versa)".

    2. It's our best guess at it working. With the huge variety of LEDs being manufactured nowadays, we don't have the manpower to test them all. The PD-6ANS switch always works fine with incandescent or halogen bulbs. With the way digital dimmers/switches work, there can still be a very small amount of voltage on the output of the switch, even when the switch is off, to keep the microchip running. Incandescent or halogen bulbs aren't affected by this small voltage, but some LEDs are sensitive enough to pick up on this voltage and stay lit at a very dim level. The LUT-MLC helps with this small voltage.
    I have a chandelier with 3 Philips Warm Glow LEDs, which should be compatible. I am also having the problem with dim illuminatin when the PD-6ANS is "off". When it is "off" I am measuring about 23VAC between the load and neutral. That is a lot of voltage for it being "off". Is my unit defective? And, if I were to add a LUT-MLC, and that fixed the problem, how much power leakage would I experience while it was "off"?
    thanks.
    Last edited by palo_alto_diy; 02-26-2018 at 02:38 AM. Reason: typo

Similar Threads

  1. LEDs connected to PD-6ANS flash when OFF
    By Justin.coolDallas in forum Troubleshooting - CAS
    Replies: 14
    Last Post: 10-25-2018, 11:03 PM
  2. PD?6ANS and a Pico
    By Otharcharr in forum General Discussion - CAS
    Replies: 2
    Last Post: 01-19-2017, 12:45 PM
  3. PD-6ANS help
    By Kzooray in forum Troubleshooting - CAS
    Replies: 5
    Last Post: 10-17-2016, 04:32 PM
  4. Turning off the status LED
    By Bktay in forum General Discussion - RA2
    Replies: 2
    Last Post: 10-14-2014, 12:02 PM
  5. Mains voltage dimmable LEDs vs Low Volatge dimmable LEDs with transformers
    By etienneterblanche in forum General Discussion - LED
    Replies: 5
    Last Post: 09-17-2014, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •