    Centralite Elegance System

    Has anyone replaced a Centralite Elegance Lighting System?

    What exists are:
    (15) Keypads, (2) Table Top Wired Keypads
    Coleman Cable 67005 22awg 6/C Wire (Shielded & Stranded, not Twisted), looks like 2 Keypad loops
    (1) Large Panel w/ (36) D2425-10 Blocks
    (1) Elegance Master Controller

    What worries me most is the wire lengths in the panel, if I swap it out to a PNL-8. Actually considering just using dimmers of WPMs.

    Any does or don'ts would be appreciated.

    Thanks, Betsy V.

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    I would consider RR2. The RR2 keypads can be powered by 48vdc. There is an app note on the Lutron site. It sounds like you only have a few zones. With dimmers you have the option of the 6CL, 6ND, & 6NA. That gives you a lot more LED options. If the loads are LED you can put the dimmers in 4-gangs with minimal derating effect.

    The WPM will only do forward phase. If you use WPMs, each zone of the WPM counts as one device.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com