    Interactive database extraction issue

    Hi there,

    I'm trying to extract a data base from an interactive processor using a direct connection but about 2/3 of the way through it stops and I get the following rotating display in the diagnostic display d/01/05/32/99?
    I've tried different baud rates as advised and even disconnected all links including the MI.
    I've also tried using the utility extraction software but still without success!! Any ideas?

    Thanks

  2. #2
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    513
    It is possible the copy of the project file stored in the processor may be too corrupted for extraction.

    The project file you extracted from the HomeWorks Illumination processor is a zipped copy of the file. This is not the same file that the processor uses to run the system. The file the system uses to run the system is stored in a different section of memory than this zipped file. It was the zipped file that is stored on the processor that what was corrupted. This is why the system is still fully functional. Unfortunately, there is not a way for us to know what caused this zipped file to be corrupted. This file could have been corrupted before it was loaded into the processor. The processor could have had a surge that damaged a section of memory where this zipped file was stores. Or it could have been any number of other causes.

    We would recommend restoring a backup copy, if one is available. If a back up copy of this file is not able to be obtained, the file will need to be re-written. Since the system is still fully functional you can connect to the processor and enable monitoring. With button and device level monitoring enabled when a button is pressed you will be able to see the address of the keypad as well as the address of the lights that responded, and the levels the lights went to. This can help in determine how the system is currently programmed.

Similar Threads

  1. Is an Upgrade of interactive to qs possible?
    By jimathome in forum Design Assistance - Legacy HW
    Replies: 7
    Last Post: 08-16-2014, 01:09 AM
  2. Project file Extraction and Baud Rate
    By Armando B. in forum Troubleshooting - Legacy HW
    Replies: 1
    Last Post: 03-25-2014, 02:01 PM
  3. Extraction
    By Vic F. in forum Programming - RA2
    Replies: 2
    Last Post: 08-29-2013, 10:51 AM
  4. HomeWorks Interactive Bridge
    By Ty W. in forum Design Assistance - Legacy HW
    Replies: 1
    Last Post: 07-30-2013, 12:11 PM
  5. XML extraction
    By Ty W. in forum General Discussion - Legacy HW
    Replies: 1
    Last Post: 07-01-2013, 02:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •