    I have just installed a new Lutron Caseta PRO Dimmer PD-10NXD replacing an operating Lutron SPSLV-600. The load is a single Iris recessed can with a 12 volt, 50 watt MR-16 lamp. This fixture includes an integral magnetic step down transformer, 120V 50/60Hz input, 12V, 50VA nominal output. I have wired the Dimmer as instructed including the white neutral. This is s single-pole installation, so the blue wire is simply terminated. See the attached image.


    All other Lutron Caseta PD-6WCL dimmers in the same J-box operate correctly. When the circuit is turned on:
    • I can detect voltage in the Blue, Black and Red wires but not the White wire
    • The lamp does not turn on.
    • Each of dimmer LED's flash on briefly from bottom to top, then after a three second delay, the top and middle LEDs begin flashing quickly.

    See the attached video.


    According to the Caseta Wireless Advanced Installation Guide, Troubleshooting, page 73, these symptoms indicate, "Product detected an MLV fault (PRO Dimmer only) • Connect Neutral to the dimmer (required for MLV load)."


    As I have connected the Neutral to the Dimmer, what do you suggest?


    Thanks so much for your help.
    Attached Thumbnails Attached Thumbnails Caseta PRO Wiring.jpg  
    Attached Files Attached Files

  2. #2
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    I have seen similar behavior in the Maestro Wireless line. Try swapping the black and red wires. When the line and load on the dimmer is incorrect, the "fixture" usually might come on very low (or not at all) and have no dimming capabilities. After the swap when this had happened, the dimmer would work fine.
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

  3. #3
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    You said it was a single pole but it appears you have it connected to a 3-wire cable. This would imply there is another switch somewhere. Or worse, a junction somewhere where they split the cable into 2 separate switch legs.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

Similar Threads

  1. Caseta ELV+/Pro with low-voltage MR16 LEDs
    By maarten in forum Troubleshooting - CAS
    Replies: 1
    Last Post: 06-26-2017, 05:14 PM
  2. Which smart dimmer for magnetic transformers w/ mix of LED & incandescent
    By TwoCoasts in forum General Discussion - LED
    Replies: 3
    Last Post: 04-13-2017, 12:03 PM
  3. Which Caseta switch to use for on/off control of 12V 50W MR16 spotlight
    By bscheffel in forum General Discussion - CAS
    Replies: 7
    Last Post: 05-03-2016, 08:10 AM
  4. dimmer on magnetic low voltage lighting ?
    By hgmobile in forum General Discussion - CAS
    Replies: 4
    Last Post: 04-12-2016, 08:11 AM
  5. Caseta Wireless 600-watt/150-watt Multi-Location In-Wall Dimmer
    By calirap in forum General Discussion - CAS
    Replies: 1
    Last Post: 01-06-2016, 09:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •