Is there anyway to change the pulse setting to any timing in HWQS?
Currently, the pulse timing is limited to 0.25s, 0.5s, 0.75s, 1.0s, 2.0s, 5.0s, 10s, 20s.
Are we able to input this or change the settings manually.
We are controlling Somfy Shades (not our preference as they are so much cheaper than Lutron Shades) now, and was told that we should not pulse more than 3 secs else their Somfy Moco Controller will go into setup mode.
Pulsing 2.0s does not work but it works for 5.0s. We do not want to end up entering their setup mode.
We are hoping that we can try a 3s pulse to see if it works and not end up entering their setup mode.
Thank you for this feedback, for Pulsed CCO loads you will be able to select one of the times that are listed in the software. To accomplish a pulsed time that is not listed you can use a maintained closure and program use an automatic sequence to set you pulsed time.
Attached is a sample project file programmed to close a contact closure output for 3 seconds and then open it using an automatic sequence. The load is defined as a maintained closure. On the first step of the sequence the CCO is closed. The option to automatically move to the next step is select and the time is set for 3 seconds. The second step has the maintained CCO opened.