3-Wire LED Light Fixture
Hello,
I'm new here, so I apologize in advanced if my question is not clear.
I'm designing a HomeWorks QS system and need to confirm the load type and the correct control parts required for the system to work properly.
I have a LIGHTHEADED downlight fixture that calls for "Lutron 3-Wire (1%)" and I selected the load type as "LED 3-wire". When I'm landing the loads in the modules it automatically adds a "PHPM-3F-120" interface at each output.
Is there another way around it? Or this is the only way to do it right?
Am I selecting the wrong load type? I was going to attached the light fixture spec, but couldnt do it.
The fixture is: LIGHTHEADED L4X-F-RA
Thank you,
Miguel.
-
There is other ways of doing accomplishing 3 wire dimming with QS. However they will all require more hardware. For example they offer 3 wire RF dimmers but since you already have a RPM panel the PHPM-3F-120 is a better choice
The real issue here is that the wrong type of driver was selected for the fixture when using this fixture with Lutron Homeworks They do offer 2 wire dimming where it could have been used direct wire to the RPM. The down is the dimming range usually only down to 10% vs 1% on 3 wire or Eco
I would recommend familiarizing yourself with LED dimming types If these fixtures and Qs were designed as a system you may have been able to give a less expensive setup with better control using Lutron Eco. Most likely these fixtures were specified by a designer with no consideration for control and dimming. I understand your pain !! been there and once you get more familiar with LED dimming types it will give you a huge understanding of the LED world where there are no standards and its everyman for himself. LOL
-
Post Thanks / Like - 0 Thanks, 1 Likes, 0 Dislikes
-
Thank you so much for your prompt response!
The light fixtures are being provided by the electrical contractor and we had specified a QS system to put the proposal together before the cut sheets were available. I believe there is still time for them to change the fixture specifications.
It would be a lot easier if we were also providing the fixtures.
-
Post Thanks / Like - 0 Thanks, 1 Likes, 0 Dislikes
-
Oops
clicked and responded before realizing I was in a HWQS sub-forum. Sorry!
Last edited by SDR-Mike; 08-28-2017 at 03:50 PM.
Reason: wrong forum