    I installed a Caseta In-Wall dimmer PRO PD-10NXD to replace an appropriate Diva dimmer for a
    Tu Wire ballast, 2 T8 4' fluorescent fixture. Previously worked like a charm.

    I very carefully reviewed the tech doc before going ahead, and it is listed as compatible, no neutral required.

    I works fine (adjusted with trims) except that when I push the "off" button it turn off but after 1-5 seconds will automatically turn back on, at a low level. I can recreate within the iOS app, when turned off, then adjusting to 1% it turns off, then back on, then adjusting to 2% it turn off again, then back on.

    It's been like that for a couple of weeks. I found the LUT-MLC used by the switches for low loads and wonder if it would work.

  2. #2
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    628
    The LUT-MLC was never tested for use with a dimmer. It was only tested for use with the on/off switches, like the PD-5WS-DV.
    What is the model number of the ballast?

  3. Thanks Yanicking thanked for this post
  4. #3
    Junior Member
    Join Date
    Jul 2017
    Posts
    5
    Hi, It would be a 2W-T832-2, bought in end-2011.
    Another thing to know is that both the dimmer and fixture are installed in an older home with no bonding/grounding conductor, if it is of interest.

  5. #4
    Junior Member
    Join Date
    Jul 2017
    Posts
    5
    Sorry 2W-T832-120-2

  6. #5
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    628
    On the PD-10NXD, did you connect the white neutral dimmer wire to a neutral bundle in the wallbox?
    The dimmer will work without a ground connection, but for any load other than an incandescent or halogen, the dimmer neutral needs to be connected.

  7. Thanks Yanicking thanked for this post
  8. #6
    Junior Member
    Join Date
    Jul 2017
    Posts
    5
    Well thank you.
    Is there an resolution if the wall box does not have a neutral in it ? I believe that only two wires come in the box. I might have a neutral in the ceiling box. The neutral is used to power the control circuit I imagine ?

Similar Threads

  1. Zone intermittently Turns On By Itself-Can't be turned off
    By DHKaplan in forum Troubleshooting - Legacy HW
    Replies: 5
    Last Post: 05-23-2017, 12:51 PM
  2. RA2 Maestro Dimmer for Lutron Tu-Wire ballast
    By Dimerize in forum General Discussion - RA2
    Replies: 2
    Last Post: 02-05-2016, 06:38 AM
  3. Replies: 1
    Last Post: 10-26-2015, 03:25 PM
  4. Replies: 1
    Last Post: 08-31-2015, 11:24 PM
  5. 6NA dimmer controlling Philips Mark 10 powerline ballast?
    By digit1 in forum General Discussion - HWQS
    Replies: 0
    Last Post: 04-07-2015, 12:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •