Originally Posted by
Craig W.
Since in the location this system is being installed in does not support HomeWorks spec grade panels you would need to put a PNL-8 in the software. The panels that are on site would need to have either an MI’s or SPI’s installed in them. Also for every 32 circuits the panel a MI or SPI would be needed.
In the HomeWorks QS software for each MI or SPI you would add a PNL-8. You would add RPM-4U’s to the panel and each output would represent the corresponding circuit in the panels that are on site. So RPM 1 output 1 would be circuit 1. RPM 2 output 1 would be circuit 5.