Thread: Processor Link blink codes

  1. #1
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    22

    Processor Link blink codes

    We received this question from a customer, and thought others might be interested in this topic...

    Is there a way to tell what type a link is programmed to the proc by how the led blinks on L1 or L2?

  2. #2
    Authorized Lutron Contributor
    Join Date
    Apr 2013
    Posts
    403

    RE: Processor Link blink codes

    There is not a set blink code for each link type as depending on if the processor is send or receiving information will determine what the TX/RX LED will be doing.

  3. Likes Ty W. liked this post
  4. #3
    Authorized Lutron Contributor
    Join Date
    Jun 2013
    Posts
    19
    Quote Originally Posted by Craig W. View Post
    There is not a set blink code for each link type as depending on if the processor is send or receiving information will determine what the TX/RX LED will be doing.
    While this is true, there are some things you can tell. For example, the MI link is a streaming protocol so the TX/RX LED is continuously flashing. The RF link tends to flutter when there is communication while the QS link TX/RX tends to stay on a little longer.