Thread: HVAC Controller "smarts"

  1. #1

    HVAC Controller "smarts"

    Hi: If you your daily schedule says to set the "Wake" temperature for X, will the system simply adjust the setpoint at that time, or will it learn and adjust the setpoint in advance so the measured temp is X at the "Wake" time?

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    433
    I dont believe Lutron stats actually learn Lutron engineers would have to comment on that. There are temperature control systems that do that especially in hydronic heating. There are many reasons systems will learn what it takes to heat or cool a room. The factors mostly involved are outside air temperature which drives water temperature used to heat. Another contributing factor is when a mass is heated such as a slab it will radiat heat well after the heat is turned off. Generally on a less technical system we would use just a outdoor reset controller to adjust water temperature. In more advanced set up we use communicating stats which tell the system all the parameters it took and how long it took to bring a space to set point. The controller learns from that and constantly adjust heating time and water temperature.

    Here is an example of such a system

    http://tekmarcontrols.com/images/_li...e/i0000_11.pdf

  3. #3
    Authorized Lutron Contributor
    Join Date
    Aug 2013
    Posts
    109
    ekimla, Lutron's HVAC Controller does indeed have "smarts" built into the product where it will learn over time how long it takes to get the temperature to the programmed setpoint level. For example, if you program a "wake" mode for 6 AM to set the temperature to 70 degrees and the system learned over time that it takes approximately 20 min. to reach that temperature level, the system will call for heat/AC at 5:40 AM to get the temperature to 70 degrees at 6 AM. Note that this functionality only exists with Lutron's HVAC Controller, not the TouchPRO wireless thermostat.

  4. #4
    Thanks Eric. So I guess this smart feature applies only to the daily schedule (not regular timeclock events) and also applies to RA2?

  5. #5
    Authorized Lutron Contributor
    Join Date
    Aug 2013
    Posts
    109
    Quote Originally Posted by ekimla View Post
    Thanks Eric. So I guess this smart feature applies only to the daily schedule (not regular timeclock events) and also applies to RA2?
    That is correct. The feature applies to HVAC schedules programmed on the "program > thermostat" screen in both HWQS and RA 2. The feature does not apply to temp. adjustments triggered via timeclock events.

  6. Thanks ekimla thanked for this post

Similar Threads

  1. HWI phantom buttons and HWQS "Virtual" keypads
    By LightBrigade in forum Programming - HWQS
    Replies: 12
    Last Post: 05-28-2014, 12:24 PM
  2. HVAC Controller
    By ekimla in forum Programming - HWQS
    Replies: 5
    Last Post: 04-28-2014, 09:55 PM
  3. HQWS and "Auto" device feature
    By thefish in forum General Discussion - HWQS
    Replies: 3
    Last Post: 11-02-2013, 03:36 PM
  4. "Unaffected" invisible in Level Editor
    By LightBrigade in forum Programming - HWQS
    Replies: 1
    Last Post: 10-15-2013, 11:25 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •