Can a GRX-TVMKIT-120 work with HW-RPM-4R
I spoke to numerous lutron techs regarding using a 4r RPM with a TVMKIT. Some say 4Rs can be used other disagree. I could use a 4A or 4U of course but with the amperage (8A) of each light I would need to have twelve (12) RPMs. If indeed i can use a 4R how do i put it into the program?
-
I have used 4R Just put it in as a 4A The On Off worked fine for me
-
If I pull 0-10 wire also can i dim the loads?
-
Yes
If you don't need to turn off 110 volt to the led driver then an rpm is not even necessary However just because you don't use and rpm module for the Led driver you will still loose the ability to use that rpm zone for anything else For every TVM you install and depending where on the harness you plug it in you will loose the ability to use those 2 zones for anything else other then that specific 0-10 zone I hardly ever need the rpm with todays drivers . Hope this helps don't forget you also have the ability to do dim 0-10 wireles with the rf 0-10 modules
-