RPM-4R - Address Switch Position F
Have a client that wants to remove the switched outlet function from the system and make them always hot. This involves all outputs of a number of RPM-4R's.
Is there any reason not to just have the caretaker change the dial to F on the RPM? Manual for the RPM states position F is to be used for "temporary" testing of loads. Curious if there are side affects to choosing this route.
Alternative would be to install the jumpers in the block but I am not sure if they are onsite (even though the should be).
-
Hello totesthouse,
Thank you for your post.
You could activate the RPM dial to the all on position. Using the jumpers may be a better solution as you can bypass the RPMs to prevent any damage to the modules in the future from power events.
-