    RRD-6NA - will switch on/off but not dim.

    Not a bulb issue as the same bulbs are used elsewhere on 6Na. When the switch is 1% to 100% the lights are 100% on and pop off when switched to 0% when on reverse phase, ie do not dim 100% on at any dim level. Change to forward phase and the lights do not function at all. I'm thinking a wiring issue as affect 4 out of 20+ switches and the four are in a single area, any ideas?

  2. #2
    Junior Member
    Join Date
    Jul 2016
    Posts
    4
    Power cycling the switches seems to have solved the problem

  3. #3
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    289
    Hi Steephen, the symptoms you explained sound like it may be something with the load causing the dimmer to falsely go into a protective mode. Power cycling the dimmers clears the fault, but it could happen again depending on the lights being used.