Thread: House Has No Ground Wires

  1. #1
    Junior Member
    Join Date
    May 2016
    Posts
    2

    House Has No Ground Wires

    I'm replacing existing Lutron dimmers in an old house with Caseta dimmers. I discovered that the green screw on the existing dimmers isn't connected to anything. The other three wires are the same color. The wall box is metal. Should I simply cap off the green ground wire on the Caseta dimmer and otherwise install per the instructions? I would assume this would still work and would be as safe as what I have currently, but I'm no electrician. I would very much appreciate guidance.

  2. #2
    Senior Member
    Join Date
    Jul 2014
    Posts
    120
    Are there ground wires in the wall box? They'll be bare copper with no insulation. If so, connect the green terminal on the Caseta to them.

  3. #3
    Junior Member
    Join Date
    May 2016
    Posts
    2
    No, there is no bare copper ground wire.

  4. #4
    Authorized Lutron Contributor
    Join Date
    Jul 2015
    Posts
    112
    Quote Originally Posted by Oakley View Post
    I'm replacing existing Lutron dimmers in an old house with Caseta dimmers. I discovered that the green screw on the existing dimmers isn't connected to anything. The other three wires are the same color. The wall box is metal. Should I simply cap off the green ground wire on the Caseta dimmer and otherwise install per the instructions? I would assume this would still work and would be as safe as what I have currently, but I'm no electrician. I would very much appreciate guidance.
    Yes, simply cap the green wire on your Caseta device.

  5. #5
    Since you have metal boxes it sounds like your house is wired with BX cable; the type of cable that has a metal sheathing. In that case the metal sheathing acts as a ground.

  6. #6
    Senior Member
    Join Date
    Nov 2014
    Posts
    238
    It may also have old cloth romex with an unsized ground wire terminated on the exterior of the metal box. Grounding the dimmer to the box is the best option. It may also be possible to attach a ground tail to the metal box and connect it to the dimmer. Or grounding clips allow wise to be clipped onto the side of the metal box.

  7. #7
    Senior Member
    Join Date
    Dec 2013
    Posts
    579
    Quote Originally Posted by AJF4ME View Post
    Since you have metal boxes it sounds like your house is wired with BX cable; the type of cable that has a metal sheathing. In that case the metal sheathing acts as a ground.
    Many older houses have metal boxes and still have either knob and tube wiring or the old cloth NM cable without a ground. I seriously doubt this house has a proper ground - unbroken bonding to the panel, connected bonding jumper at the panel, and a ground rod. Never assume grounding just because there is a metal box.

  8. Likes K-n-C liked this post

Similar Threads

  1. multiple smart bridge pros in the same house?
    By MCHAMMER in forum General Discussion - CAS
    Replies: 25
    Last Post: 01-07-2017, 02:47 PM
  2. Interesting RA2 Install in +$5mm house
    By Yetis in forum General Discussion - RA2
    Replies: 8
    Last Post: 08-09-2016, 05:17 PM
  3. (mostly) Whole-house installation COMPLETE!
    By asherrick in forum General Discussion - CAS
    Replies: 13
    Last Post: 01-08-2016, 05:20 PM
  4. so an integrator walks into a house.....
    By jkvossen in forum Troubleshooting - Legacy RA
    Replies: 1
    Last Post: 01-26-2015, 06:56 PM
  5. two wire switch no ground no neutral wires UMS-OPS6M-DV-WH
    By dfphoto in forum General Discussion - Controls
    Replies: 0
    Last Post: 11-21-2014, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •