Thread: HWQS connect GP Panel with circuit selector

  1. #1
    Junior Member
    Join Date
    Jul 2015
    Posts
    3

    HWQS connect GP Panel with circuit selector

    Dear Support Team,

    Is it possible to replace the circuit selector to MI card for the connection of HWQS system?

  2. #2

    SPI for GP Panel

    Quote Originally Posted by Syncon View Post
    Dear Support Team,

    Is it possible to replace the circuit selector to MI card for the connection of HWQS system?
    You would use a HomeWorks SPI, which is the Spec Grade Panel Interface, in place of the circuit selector. Keep in mind that the SPI supports 24 loads, so you may need more than one, just like the circuit selector, if you have a panel larger than 24 circuits.

    Each SPI counts as one of your Panel Addresses.

  3. #3
    Junior Member
    Join Date
    Jul 2015
    Posts
    3
    Thank you for your explanation! If the project is is use 240v version, is it the model replaced with HWI-MI-230?

  4. #4
    Check with Lutron Tech Support. That is not the model number. It will be the SPec Grade Panel Interface for 230V countries. This is not the same as the MI.

Similar Threads

  1. 2Link Circuit selector version for Homeworks QS available ?
    By eickhoff in forum General Discussion - HWQS
    Replies: 7
    Last Post: 01-23-2017, 05:19 PM
  2. Replies: 8
    Last Post: 05-18-2016, 06:47 PM
  3. Replies: 1
    Last Post: 12-10-2014, 11:28 AM
  4. Replies: 5
    Last Post: 10-20-2014, 10:52 AM
  5. HWQS Feed Thru Panel
    By Fitz1 in forum General Discussion - HWQS
    Replies: 1
    Last Post: 06-18-2014, 12:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •