    Question Non-conventional loads on Caseta switches

    Folks, client is asking to connect a small 3A towel dryer to a Caseta switch, so that it can be entered into a schedule. Makes sense from a customer experience standpoint, however my sense is that Caseta switches are only for lighting loads and fans. Client also wants to know whether the switch can also be connected to a floor heater for the bathroom (8A in this case). Any insights would be appreciated.
    Thanks!

  2. #2
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    635
    You are correct. Our Caseta switches are only rated for lights and fan loads. I wouldn't ever recommend trying to use it for a towel dryer, floor heater, or anything that isn't a light or a fan. We can't guarantee how it would work with other loads, or even how long it would last with those loads.

  3. Thanks Dimerize thanked for this post
    Likes Dimerize liked this post
  4. #3
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    Brian W.- What is the official word on running a PD6ANS controlling a contactor to control these loads? We've used RRD8ANS many times in RR2 like this with no troubles.
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

  5. Thanks Dimerize thanked for this post
    Likes Dimerize liked this post
  6. #4
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    635
    Quote Originally Posted by SanDiegoRep View Post
    Brian W.- What is the official word on running a PD6ANS controlling a contactor to control these loads? We've used RRD8ANS many times in RR2 like this with no troubles.
    The official word is the PD-6ANS is only UL rated for the load types listed on page 2 of the spec sheet: http://www.lutron.com/TechnicalDocum...369831_ENG.pdf . Lights and fan motors only. It "may" be able to switch other loads, but we don't test it for anything other than lights and fans.

  7. Thanks SDR-Mike thanked for this post

Similar Threads

  1. Deleting Dimmers or switches from Caseta system?
    By ntwkdsnr in forum General Discussion - CAS
    Replies: 5
    Last Post: 10-06-2022, 01:57 PM
  2. Caseta Pro Switches
    By mark2457 in forum General Discussion - CAS
    Replies: 31
    Last Post: 04-01-2020, 01:48 AM
  3. Switch florescent loads on/off (no dim)
    By mark2457 in forum General Discussion - RA2
    Replies: 1
    Last Post: 11-04-2015, 03:24 PM
  4. Assigning Loads in QS 8.3
    By Kevin Craig in forum Design Assistance - HWQS
    Replies: 2
    Last Post: 08-17-2015, 06:18 PM
  5. loads not responding
    By Craig W. in forum Troubleshooting - HWQS
    Replies: 1
    Last Post: 05-22-2013, 07:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •