Thread: Occupancy Sensor MS-VPS5M - troubleshooting sensitivity setting

  1. #1
    Junior Member
    Join Date
    Mar 2016
    Posts
    2

    Occupancy Sensor MS-VPS5M - troubleshooting sensitivity setting

    I installed a Occupancy Sensor, model Lutron MS-VPS5M
    I'm troubleshooting the "sensitivity setting".

    Symptom: My switch has Low / NO sensitivity even in a dark room.
    It responds OK to the switch, and the timer works OK.

    I verified with a multimeter that the installation is correct: 109VAC, 60HZ.
    The Ground connection is good.

    Programming the Timer function proceeds normally, with appropriate lamp blink codes.
    I am able to change timing per instructions, and the unit behaves properly.

    Programming the Sensitivity function function proceeds, with appropriate lamp blink codes.
    But my unit does not behave properly. It remains set on LOW sensitivity.
    It Fails to detect any motion at all, and Fails to Turn ON.

  2. #2
    Administrator
    Join Date
    Dec 2015
    Posts
    185
    Hello deecee1110,

    The model number you have, MS-VPS5M, is a vacancy sensor only. It is a manual on, auto off sensor. It will never turn on automatically. If you want a sensor that turns the lights on automatically once the room is occupied, you will go with MS-OPS5M.

    I hope this helps.

  3. #3
    Junior Member
    Join Date
    Mar 2016
    Posts
    2
    Quote Originally Posted by Jai H. View Post
    Hello deecee1110,

    The model number you have, MS-VPS5M, is a vacancy sensor only. It is a manual on, auto off sensor. It will never turn on automatically. If you want a sensor that turns the lights on automatically once the room is occupied, you will go with MS-OPS5M.

    I hope this helps.

    Thanks, this clear up my confusion. These two technical terms have very specific meaning:

    Q: What is the difference between occupancy and vacancy sensing?

    A: An occupancy sensor turn lights ON automatically upon the detection of motion then turns the lights OFF after the area is vacated.
    A vacancy sensor requires manual push-button activation of the light, then turns the lights OFF automatically after the area is vacated.



Similar Threads

  1. Occupancy Sensor Questions
    By JeffreySkalny in forum Programming - HWQS
    Replies: 1
    Last Post: 01-05-2016, 09:01 AM
  2. Occupancy sensor selection
    By Jeepdon in forum Design Assistance - RA2
    Replies: 1
    Last Post: 12-28-2015, 11:01 AM
  3. Occupancy Sensor
    By texas doc in forum General Discussion - RA2
    Replies: 4
    Last Post: 05-18-2015, 09:16 PM
  4. Occupancy Sensor Programming
    By troltgen in forum Programming - HWQS
    Replies: 0
    Last Post: 01-26-2015, 01:52 PM
  5. maestro occupancy sensor
    By Christiann in forum General Discussion - Controls
    Replies: 0
    Last Post: 07-05-2014, 04:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •