Originally Posted by
Corey S.
Adam,
You have a few options here regarding the Lutron side of things.
Using PNL8 Panels: You are correct on one account, we need to know where the line voltage 120V signal is being switched for the 0-10V fixtures. If this was being switched at the same panel (or near it) then I believe using the PNL8 with TVM2s is the way to go. However, if the line voltage for the fixtures is not being ran back to the panel then there is one other option.
Using LMJ-5T RF 0-10V Dimming Modules: This one also makes a consideration that we would need access up into the fixtures. However, if we do, then you could use LMJ-5Ts and switch the line voltage with it locally at each fixture along with controlling the 0-10V signal as well. The only consideration here is that you will need a HQP6-2 processor link set as RF with a hybrid repeater connected to it.
Beyond all of this you may need to work someone from Savant/ Litetouch. But ultimately if we know where the line voltage is landed for these fixtures then I believe we can answer a lot of questions at that point as well.