We are installing a large project with 96 Palladiom keypad units (2 and 3 gangs quickly add-up).
Then it hit us, we are gonna be short one PS (are we ?).
I don't remember seing the LED count in the QS software. Nor in QS documents am I right ?
Is there a spreadsheet somewhere or something like the old LED calculator ?
-
Post Thanks / Like - 1 Thanks, 0 Likes, 0 Dislikes
-
Authorized Lutron Contributor

Originally Posted by
mehuneau
We are installing a large project with 96 Palladiom keypad units (2 and 3 gangs quickly add-up).
Then it hit us, we are gonna be short one PS (are we ?).
I don't remember seing the LED count in the QS software. Nor in QS documents am I right ?
Is there a spreadsheet somewhere or something like the old LED calculator ?
Dear mehuneau,
Thank you for the inquiry.
The Palladiom keypads are 1 PDU per column. This information can be found in the spec sheet on page 2.
http://www.lutron.com/TechnicalDocum...369881_ENG.pdf
-