    Caseta switch no longer working - load issue?

    We have had a PD-5WS-DV controlling our outside light for almost 10 years. A few weeks ago, the light stopped working, and we figured it was the bulb, but were not able to easily change it since it is at a second story level and needs a big ladder. We changed it this weekend. The old bulb was a CFL (14 Watts). We replaced it with an Ecosmart LED (8.3 Watts). Now the light turns on, with a green led on the switch, but when we try to turn it off at the switch, it just goes dim, and all the leds on the switch go out, and it won't turn on again. The only way to turn the light completely off is to use the FASS switch. When we push that back in, the light lights up again, and same cycle.

    My research indicates that an LUT-MLC could fix this, but I can't find the one that came with the switch in 2015, so where would I get one? We do have a neutral wire, so a newer PD-5ANS might also fix the problem, but might also need the MLC, which I don't believe is included. Or a bulb that uses more Watts, although I really don't want to deal with the ladder again so soon...

    All our other Lutron switches in the house work fine, btw.

    Recommendations on the best way to fix this?

    Thanks

  2. #2
    Lutron Technical Support
    Join Date
    May 2023
    Posts
    192
    Hello Iwoody79,

    Thanks for the insight. As you stated, the recent upgrade to the LED bulb lowered the overall wattage. Since the PD-5WS-DV is not a neutral based switch, it will require that LUT-MLC to be installed on the load. You are welcome to reach out to our technical support team at support@lutron.com and we would be happy to help supply an LUT-MLC!

    This can also be resolved by installing the PD-5ANS in place of the PD-5WS-DV. Since the PD-5ANS has a neutral, and you can confirm there is a neutral bundle in the back of the box, this control does not rely on an LUT-MLC to operate with lower wattage loads.

Similar Threads

  1. Switch no longer working with LEDs
    By JMonkeYJ in forum General Discussion - CAS
    Replies: 8
    Last Post: 07-01-2024, 02:09 AM
  2. Button on ST-6B-I keypads no longer activates portion of assigned load
    By cspanpacman in forum Troubleshooting - HWQS
    Replies: 1
    Last Post: 12-18-2023, 02:03 PM
  3. PD-5S-DV no longer working with garage lights
    By sedavidw in forum Troubleshooting - CAS
    Replies: 1
    Last Post: 04-01-2021, 02:17 PM
  4. issue with dimmer not working, single switch location
    By D.B.Johnson in forum General Discussion - CAS
    Replies: 1
    Last Post: 01-02-2019, 09:20 AM
  5. Replies: 1
    Last Post: 11-21-2013, 10:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •