Thread: Rollback Programming

  1. #1

    Rollback Programming

    Trying to program a rollback (?) function on SeeTouch keypads.

    Situation is: I want to program a bathroom keypad to turn exhaust vent on (8ANS) with a scene toggle. When the button is pressed again I want the light(s) in the scene to go off, but, the vent to remain on for 15 minutes.
    I am accomplishing this with a pico in another bathroom by setting the delay to "0" for the lights, and "900s" for the vent on the Off button.
    Any ideas? I believe this was called rollback on the Ra2 software, but, admittedly cant remember.
    Thanks!

  2. #2
    Lutron Technical Support
    Join Date
    Jul 2023
    Posts
    30
    Hey there,

    Rollback feature does exist in Ra3 and will be found in Program under occupancy.
    Please note you would be setting the timeout rule for anything you have selected so keep that in mind.

  3. #3
    Junior Member
    Join Date
    Apr 2023
    Posts
    10
    Quote Originally Posted by electricrussell View Post
    Trying to program a rollback (?) function on SeeTouch keypads.

    Situation is: I want to program a bathroom keypad to turn exhaust vent on (8ANS) with a scene toggle. When the button is pressed again I want the light(s) in the scene to go off, but, the vent to remain on for 15 minutes.
    I am accomplishing this with a pico in another bathroom by setting the delay to "0" for the lights, and "900s" for the vent on the Off button.
    Any ideas? I believe this was called rollback on the Ra2 software, but, admittedly cant remember.
    Thanks!
    To program a rollback function on Lutron SeeTouch keypads, you should define a scene for the bathroom lights and set up a button to control the exhaust vent. Configure the button to toggle the scene for the lights while programming the vent to stay on for 15 minutes using a delay function. Use the Lutron software to set immediate off actions for the lights and a delayed off action for the vent, then test to ensure the functionality meets your requirements.

  4. #4
    Junior Member
    Join Date
    Sep 2024
    Posts
    1
    Quote Originally Posted by ninadobrev View Post
    To program a rollback function on Lutron SeeTouch keypads, you should define a scene for the bathroom lights and set up a button to control the exhaust geometry dash deadlocked vent. Configure the button to toggle the scene for the lights while programming the vent to stay on for 15 minutes using a delay function. Use the Lutron software to set immediate off actions for the lights and a delayed off action for the vent, then test to ensure the functionality meets your requirements.

    Sounds like a good suggestion. I will consider.

Similar Threads

  1. Rollback and occupancy sensors?
    By wkearney99 in forum Best Practices - RA2
    Replies: 5
    Last Post: 06-21-2017, 04:25 PM
  2. Where is rollback in HWQS ver 10.0
    By Pasolumination in forum Programming - HWQS
    Replies: 1
    Last Post: 08-03-2016, 03:04 PM
  3. Replies: 1
    Last Post: 11-06-2015, 10:50 AM
  4. Auto Rollback in QS similar to Illumination?
    By TomTremble in forum Programming - HWQS
    Replies: 3
    Last Post: 01-09-2014, 04:25 PM
  5. Execute Double Tap Programming without the Press programming
    By Armando B. in forum Programming - Legacy HW
    Replies: 0
    Last Post: 11-12-2013, 11:52 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •