Thread: Installing Two LUT-MLC

  1. #1
    Junior Member
    Join Date
    May 2018
    Posts
    9

    Installing Two LUT-MLC

    I am getting the red LED on one of my PD-5WS-DV-WH switches even though there is a single LUT-MLC resistor installed at the fixture. I have been told that a second resistor may be necessary for this fixture. I am thinking the two resistors should be wired in series not in parallel to get the greater resistance. Am I correct?

  2. #2
    Lutron Technical Support
    Join Date
    Jan 2022
    Posts
    139
    Hello,

    Typically only one LUT-MLC capacitor is needed per circuit. However, we have had reports of installers using 2 LUT-MLC's wired in parallel to get certain loads to work. What is the PD-5WS-DV controlling and what is the total wattage/amperage of the load?

  3. #3
    Junior Member
    Join Date
    May 2018
    Posts
    9
    I installed a second LUT-MLC in the box with the switch and things are back to normal, everything is working correctly. It was a tight fit, but I got it in there.

Similar Threads

  1. Specifying & Installing Side Channels
    By jkvossen in forum Design Assistance - Shades
    Replies: 6
    Last Post: 10-10-2023, 08:49 AM
  2. Windows WMI Error Installing Ra 2
    By Xunaria in forum Programming - RA2
    Replies: 0
    Last Post: 04-12-2023, 10:21 AM
  3. installing RRD-W6BRL
    By bomber136 in forum Programming - RA2
    Replies: 1
    Last Post: 03-16-2019, 10:21 AM
  4. Installing 15 LMJ-5T-DV-B modules in a closet
    By Dimerize in forum General Discussion - RA2
    Replies: 1
    Last Post: 04-01-2016, 11:45 AM
  5. Installing a UPS on an H8P5 processor
    By anniej in forum Troubleshooting - Legacy HW
    Replies: 1
    Last Post: 07-03-2015, 11:49 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •