    Question Processor -> switch/dimmer issue

    Hello, all.

    I have an elderly HRP5-120 processor running v1.64 with nearly 60 dimmers/switches. It has been running beautifully for many years...no complaints.

    So all is fine, except: I recently modified a project and uploaded it; several units (dimmers, switch) fail to upload properly, as noted in the log.

    HOWEVER: those units DO respond to commands from the System Control window (reached from the Terminal screen), so I know the processor can see and control them.

    Under what circumstances would this happen? How can I fix the issue?

    I have not tried un-addressing and re-addressing the units, thinking that the issue isn't really a processor-to-dimmer issue, but...I don't know. Any helpful ideas will be greatly appreciated.

    T

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,589
    This happens a lot. It usually means the software didn't get confirmation that the data was received.

    In the terminal screen, under RF/QED Device Commands, you can retry the devices that it thought had an error.

    You can also use the command SENDDB, <address> to update a single device.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  3. #3
    Junior Member
    Join Date
    Jul 2023
    Posts
    2
    Thank you, randyc!

    Quote Originally Posted by randyc View Post
    This happens a lot. It usually means the software didn't get confirmation that the data was received.

    In the terminal screen, under RF/QED Device Commands, you can retry the devices that it thought had an error.
    I confirmed the problem units with RFDBSTAT, then ran RETRYDB. Two of the three units updated, but the third did not.

    Quote Originally Posted by randyc View Post
    You can also use the command SENDDB, <address> to update a single device.
    I used SENDDB, 01:08:01:43 multiple times (6x? 8x?) on that third unit, but it still comes back as "invalid DB." I've also tried RETRYDB a couple more times, with the same result.

    T

Similar Threads

  1. Lutron Diva Smart Dimmer Switch Issue
    By ScottZ0 in forum Troubleshooting - Controls
    Replies: 1
    Last Post: 03-23-2023, 09:44 AM
  2. Issue with wiring of Lutron Diva dimmer. Original switch has 5 wires.
    By kdr2824 in forum General Discussion - Controls
    Replies: 3
    Last Post: 09-21-2020, 04:37 PM
  3. issue with dimmer not working, single switch location
    By D.B.Johnson in forum General Discussion - CAS
    Replies: 1
    Last Post: 01-02-2019, 09:20 AM
  4. Replies: 8
    Last Post: 06-16-2015, 09:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •