Thanks Thanks:  0
Likes Likes:  0
Dislikes Dislikes:  0
Results 1 to 4 of 4

Thread: MACL-153M only works once per power cycle

  1. #1
    Junior Member
    Join Date
    May 2023
    Posts
    2

    MACL-153M only works once per power cycle

    I have a MACL-153M dimmer - used in a single pole application - that only works for the first on/off cycle. Once the light has been turned off, within about 30 seconds all the IL lights on the side of the dimmer start flashing randomly. Power cycling with the FASS tab corrects the problem - until the next on/off cycle.

    I'm assuming this is a bulb compatibility issue, but I have no means of determining the bulb type. The light fixture is a Drift Linear Suspension by Modern Forms. In the absence of being able to check compatibility is there any chance that the Pro dimmer would work better?

  2. #2
    Lutron Technical Support
    Join Date
    Jan 2021
    Posts
    132
    This does sound like it could be a LED incompatibility issue and swapping out the MACL-153M could resolve the issue. Do you by chance have the model number or a link to the spec sheet for this fixture you are using? We could see if the fixture requires a specific type of dimming or something like that to give a better answer if the MA-PRO would work better.

  3. #3
    Junior Member
    Join Date
    May 2023
    Posts
    2
    Thanks Garrett. I did some digging on the manufacturer website and discovered they have done their own dimmer compatibility tests for the fixture, see Dimming Report available here.
    Since this is an ELV device they suggest the MAELVā€600, so I assume the MA-PRO will work equally well in ELV mode?

  4. #4
    Lutron Technical Support
    Join Date
    Mar 2022
    Posts
    128
    Dave, the MA-PRO is the preferred ELV LED dimmer control. The MAELV-600 was originally designed for low voltage incandescent and halogen lamps, and not LEDs in mind. The MA-PRO is newer and has updated technology that makes it better suited for dimming LEDs. By default, the MA-PRO is in ELV mode, so you should not need to make any phase adjustments to the unit. Ensure that you connect the neutral for proper functionality.

Similar Threads

  1. MACL-153M vs MACL-153MLH Maestro LED+ Dimmers
    By BBurns in forum Compatibility - LED
    Replies: 2
    Last Post: 09-02-2022, 08:17 PM
  2. Macl-153m
    By ChadArendt in forum General Discussion - CAS
    Replies: 1
    Last Post: 11-13-2020, 09:20 AM
  3. 4 way using macl-153m
    By k9jws in forum General Discussion - Controls
    Replies: 3
    Last Post: 06-29-2020, 04:10 PM
  4. New MACL-LFQW Fan/Light Switches cycle on/off
    By ChrisRosendin in forum Troubleshooting - Controls
    Replies: 1
    Last Post: 01-24-2020, 11:58 AM
  5. MACL-153M
    By Chris M in forum Troubleshooting - Controls
    Replies: 1
    Last Post: 07-11-2018, 09:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •