Thread: Flaky occupancy sensor (LRF2-OCR2B-P)

  1. #1
    Junior Member
    Join Date
    Jan 2017
    Posts
    25

    Flaky occupancy sensor (LRF2-OCR2B-P)

    Hi all,
    I have been trying to debug what I think may be a faulty occupancy sensor (LRF2-OCR2B-P) for a bit, and have had not luck figuring out what is going on.

    Here is my install.
    RadioRA3, single processor, 77 CCX devices, and 30 CCA devices.
    I have numerous occupancy sensors throughout the house, and most of them work as expected most of the time.

    The ones giving me issue are 2 setup up in the garage.
    The garage is about 800sf, 3 car garage with 2 garage doors and openers, about 11ft ceilings.
    I have 2 LRF2-OCR2B-P in the garage.
    One is on the 11ft ceiling closer to the south side of the garage, and the other is about 8ft up, on the north side.
    These are programed as occupancy, to turn on the garage lights on occupancy and turn off the lights on vacancy.

    This is what is happening:
    Right after I do a system transfer, the sensor occupancy works, and the lights turn on. But Vacancy never turns off the lights.
    If I push the light button the sensors, the lights turn on and off. If I use the test button the sensors, it picks up movement just fine.
    The occupancy only works one time after I do a system transfer

    When I look at the event logs right after a system transfer, I see the following (highlighted in green are the garage events)
    Click image for larger version. 

Name:	Screenshot 2024-04-01 231826.png 
Views:	5 
Size:	75.0 KB 
ID:	1142
    But the vacancy never fires the ACTIVATE PRESET part, so the vacancy never turns off the lights.

    I waited a bit and then tried to trigger the occupancy again, all I got was one event
    Click image for larger version. 

Name:	Screenshot 2024-04-01 232323.png 
Views:	5 
Size:	32.5 KB 
ID:	1143

    The garage design is as follows
    Click image for larger version. 

Name:	Screenshot 2024-04-01 232616.png 
Views:	5 
Size:	64.5 KB 
ID:	1144

    And the programming like this
    Click image for larger version. 

Name:	Screenshot 2024-04-01 232740.png 
Views:	6 
Size:	22.4 KB 
ID:	1145
    Click image for larger version. 

Name:	Screenshot 2024-04-01 233040.png 
Views:	5 
Size:	22.3 KB 
ID:	1146

    Anyone else run into issues with occupancy sensors like this?

    What other debugging would you suggest?

    Thanks

  2. #2
    Junior Member
    Join Date
    Jan 2017
    Posts
    25
    Had a long call with tech support last night - and got some of it working.
    We essentially removed, factory reset the sensors and added them back in.
    The results - if I have only 1 sensor in the area, it works as expected, once I add the second sensor it stops working.

    Question for other installers/owners: do you have an area with 2 Occupancy sensors working properly ?

Similar Threads

  1. Lutron LRF2-OCR2B-P-WH
    By radioRA2automation in forum Troubleshooting - RA2
    Replies: 2
    Last Post: 03-07-2022, 02:42 PM
  2. Replies: 12
    Last Post: 11-13-2020, 06:53 PM
  3. LRF2 Vacancy sensor & manual switch usage
    By MisterC in forum General Discussion - RA2
    Replies: 7
    Last Post: 04-07-2017, 07:38 PM
  4. Replies: 4
    Last Post: 02-09-2017, 10:28 AM
  5. Querying Occupancy Sensor (LRF2-OC) and Remote Temp Sensor (LRF2-TWRB)
    By Fiasco in forum 3rd-party Integration - RA2
    Replies: 7
    Last Post: 11-12-2016, 07:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •