Thread: Issues with MRF2S-8SS - switch only - no dimmer

  1. #1
    Junior Member
    Join Date
    May 2022
    Posts
    18

    Issues with MRF2S-8SS - switch only - no dimmer

    The switch is in my garage. There aren't any HVAC vents in the garage. There aren't any hot items such as a recently driven car, etc.

    Issue 1
    I have the timeout set to 1 minute (have tried other time settings too). The lights will not turn off automatically regardless of whether the switch turns on manually or automatically. The only troubleshooting thing I can find is to check for "noise" such as an HVAC vent.

    Issue 2
    I would like the auto on function to work regardless of how much ambient light is perceived by the switch. I have the Fixed ALD level set to "High". They aren't coming on automatically during the day. Is there a way to turn this off so it doesn't take ambient light into account?

  2. #2
    Junior Member
    Join Date
    May 2022
    Posts
    18
    Regarding issue 2, I've found where one can change the setting to learning ALD so I'm working on that. Still need to solve issue 1.

  3. #3
    Junior Member
    Join Date
    May 2022
    Posts
    18
    50+ views and no one has any suggestions as to why the timeout doesn't work?

  4. #4
    Lutron Technical Support
    Join Date
    Jul 2021
    Posts
    25
    Thank you for your post, DIY22.

    For issue #1, we recommend keeping the timeout set for one minute and grabbing something to cover the sensor lens with (towels, shirts, etc.) so that your hand cannot be picked up by the passive infrared sensor, and start a one minute timer. After 60 seconds, does the load turn off?

  5. #5
    Junior Member
    Join Date
    May 2022
    Posts
    18
    Yes, the load turns off. I tested several times and they all turned off within about 60 seconds.

  6. #6
    Junior Member
    Join Date
    May 2022
    Posts
    18
    So, what does this test mean? Interference somehow? As mentioned, there aren't any HVAC vents. It is more than 10ft from the LED ceiling lights.

  7. #7
    Lutron Technical Support
    Join Date
    Jul 2021
    Posts
    25
    Since the load did turn off while using something opaque to cover the sensor lens, the Maestro is functioning as it should. This would point to an environmental issue, where something within the sensor's field of view or in close proximity is being interpreted as movement and not allowing the timeout to occur. Aside from any HVAC venting, other factors to consider are network equipment, such as wireless routers or wireless access points.

  8. #8
    Junior Member
    Join Date
    May 2022
    Posts
    18
    None of those are close by either. I'm having great difficulty in getting the light to come on too. I thought the learning ALD function would fix it but not having a lot of luck there either. Would a LRF2-OWLB-P function the same way regarding the amount of ambient light and turning on? Does it look at ambient light before functioning? Maybe I could just use a switch that allows control with a LRF2-OWLB-P. Any thoughts?

  9. #9
    Junior Member
    Join Date
    May 2022
    Posts
    18
    Well, I went out to the garage 3 times last night after dark. The sensor would not turn the light on even when I waved my hand inches from it. Yesterday morning when I went out to the garage, the light was on so I assume it was on all night. I'm now thinking that I have a defective switch/sensor. If I press the button on the switch, the light will work.

  10. #10
    Lutron Technical Support
    Join Date
    Jan 2021
    Posts
    127
    Hi,

    Please give our Technical Support team a call at 1-888-588-7661. We would be able to go over more detailed troubleshooting steps to see if it's the sensor or if there's something else causing the issue.

Similar Threads

  1. Maestro dimmer and companion issues
    By ScottK in forum Troubleshooting - Controls
    Replies: 2
    Last Post: 04-12-2020, 06:24 PM
  2. Issues with Caseta Lamp Dimmer PD-3PCL-WH
    By asgallant in forum Troubleshooting - CAS
    Replies: 1
    Last Post: 02-02-2020, 10:13 AM
  3. MRF2S-8SD010-XX—0-10 V dimmer sensor
    By heatman5 in forum General Discussion - RA2
    Replies: 1
    Last Post: 09-16-2019, 10:59 AM
  4. Issues with Nova-T dimmer and/or PP-20 Power Pack
    By Patchen in forum Performance Issues - LED
    Replies: 4
    Last Post: 05-03-2018, 10:05 AM
  5. 3 way switch circuit --> Lutron dimmer replacement issues
    By Subdermal in forum Troubleshooting - Controls
    Replies: 4
    Last Post: 12-13-2017, 11:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •