    After config transfer, module doesn’t respond HWQS

    ​So this is in HWQS version 14.3 and 15.10.1 on two different sites and using different computers I have come across what could be a related bug but I’m still unsure. It’s all wired with QS cable and both sites are about 6 years old.

    Effectively a client wants a quick change to a scene and I do a transfer. The program says its ok with no errors, I restart the program to do Diagnostics > Verify Devices, all green tick.

    Client then uses an unrelated part of the system and finds a light or zone won’t turn on. Manual test of the zone is ok, verify the load in software and nothing happens. Find that a whole switching module having issues but it is ok in the program but not turning things on.

    So I re-transfer the same unedited config, no errors, verify devices, all green. The module now works.

    Sometimes a re-transfer doesn’t work even though everything says it’s ok, the “printconnecteddevices” command says everything is fine. What might be happening and is there better diagnostics? Do I need to do firmware updates on the modules affected?

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    Are they DIN or RPM module? I'd look at the wiring.

    I'd also try transferring via wired connection.

    I'd also use the app for a "quick change."
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  3. Likes jasonma liked this post
  4. #3
    Junior Member
    Join Date
    Sep 2017
    Posts
    6
    DIN module and it was a wired transfer. Also they were conditional buttons for the quick update so no way around that yet.

    After a little more poking around I put it on full monitoring and found these messages after telling the module to turn on the loads:

    Timed out waiting for IPL acks.
    Bitmap of ACKs missed: 00000000 00000000 00000000 08000000

Similar Threads

  1. is the PowPak EcoSystem module RMJ-ECO32-DV-B available for HWQS?
    By steven1454 in forum General Discussion - HWQS
    Replies: 1
    Last Post: 04-13-2021, 10:47 PM
  2. HWQS Database Transfer Stopping at 94%
    By AndyTurnerMaui in forum Troubleshooting - HWQS
    Replies: 3
    Last Post: 11-02-2019, 03:16 PM
  3. Hybrid Keypad initial button config vs engraved button config
    By gt3mike in forum Design Assistance - RA2
    Replies: 6
    Last Post: 05-09-2019, 12:21 PM
  4. Lite Touch to HWQS Module cross reference
    By Mike Greene in forum General Discussion - HWQS
    Replies: 2
    Last Post: 03-03-2017, 05:51 PM
  5. Event scheduling does not respond
    By JoseSD in forum Troubleshooting - HWQS
    Replies: 1
    Last Post: 02-11-2017, 12:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •