After config transfer, module doesn’t respond HWQS
​So this is in HWQS version 14.3 and 15.10.1 on two different sites and using different computers I have come across what could be a related bug but I’m still unsure. It’s all wired with QS cable and both sites are about 6 years old.
Effectively a client wants a quick change to a scene and I do a transfer. The program says its ok with no errors, I restart the program to do Diagnostics > Verify Devices, all green tick.
Client then uses an unrelated part of the system and finds a light or zone won’t turn on. Manual test of the zone is ok, verify the load in software and nothing happens. Find that a whole switching module having issues but it is ok in the program but not turning things on.
So I re-transfer the same unedited config, no errors, verify devices, all green. The module now works.
Sometimes a re-transfer doesn’t work even though everything says it’s ok, the “printconnecteddevices” command says everything is fine. What might be happening and is there better diagnostics? Do I need to do firmware updates on the modules affected?
-
Are they DIN or RPM module? I'd look at the wiring.
I'd also try transferring via wired connection.
I'd also use the app for a "quick change."
-
Post Thanks / Like - 0 Thanks, 1 Likes, 0 Dislikes
-
DIN module and it was a wired transfer. Also they were conditional buttons for the quick update so no way around that yet.
After a little more poking around I put it on full monitoring and found these messages after telling the module to turn on the loads:
Timed out waiting for IPL acks.
Bitmap of ACKs missed: 00000000 00000000 00000000 08000000