0-10v lmj-5t-dv-b
I am thinking of using the above because the electrician (not me) has a switch leg with 20 recessed lights on it. The 0-10 V has a max of 60MA. Does anyone know how many MA each fixture's o-10V input uses? I have asked WAC engineering but am getting tired of waiting for their answer.
Thanks!
-
Originally Posted by
Bill13
I am thinking of using the above because the electrician (not me) has a switch leg with 20 recessed lights on it. The 0-10 V has a max of 60MA. Does anyone know how many MA each fixture's o-10V input uses? I have asked WAC engineering but am getting tired of waiting for their answer.
Thanks!
2 mA per fixture max per fixture is good rule of thumb. You should be fine especially if the fixtures are all the same model (same internal resistance of the 0-10 volt reference)
-