    Question Skylark Contour not working?

    I have a 120v 3-way switch set-up controlling some LED lights which are dimmable. I am attempting to replace one of the existing standard switches with a Lutron Skylark Contour. The existing configuration looks like this:

    Click image for larger version. 

Name:	3way.png 
Views:	2 
Size:	280.4 KB 
ID:	910

    I connected the new Skylark in the switch position indicated in the diagram as follows:
    Lutron green wire --> Ground
    Lutron black wire --> Common wire (Black wire from incoming power feed)
    Lutron red wire --> red traveler to other switch
    Lutron red/white wire --> black traveler to other switch
    (The two white were left connected as they were)

    I turned the power to the circuit back on at the panel and... nothing. I flipped both switches on and off in all possible combinations and the light never went on. The dimmer slider was all the way up, but I moved it around as well. Nothing.

    I thought perhaps I had received a defective dimmer, so I got another one. I installed it the same way and it also did not work. I also tried reversing the two travelers (which shouldn't make a difference.) I double-checked the other switch and it is connected as shown in the diagram. I removed the Lutron and reconnected the old switch and it all works fine.

    What could be the issue?

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    I'm sure you have done this but... verify that the wires connected to the red and red/white are from the same cable. It's easy to get the blacks swapped and it won't work if you do.

    The dimmer has a minimum load requirement. It's typically 1 LED but it may be more depending on the type of bulb you are using.

    Most Contour dimmers are forward phase. If your bulbs require reverse phase you would need a reverse phase dimmer.

    There is a small trim adjustment knob on the side. Start with it in the middle position.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  3. #3
    Junior Member
    Join Date
    Jan 2022
    Posts
    2
    Quote Originally Posted by randyc View Post
    I'm sure you have done this but... verify that the wires connected to the red and red/white are from the same cable. It's easy to get the blacks swapped and it won't work if you do.

    The dimmer has a minimum load requirement. It's typically 1 LED but it may be more depending on the type of bulb you are using.

    Most Contour dimmers are forward phase. If your bulbs require reverse phase you would need a reverse phase dimmer.

    There is a small trim adjustment knob on the side. Start with it in the middle position.
    Thanks for the reply-- I hooked up a different brand dimmer and it all worked on the first try. I suspect it may be one of the issues you suggested re: phase or trim adjustment.

Similar Threads

  1. Replacing old GE 3-way dimmer with Skylark Contour
    By larry64 in forum General Discussion - Controls
    Replies: 2
    Last Post: 12-21-2020, 12:52 PM
  2. Lutron Skylark Dimmer
    By GlennSav in forum General Discussion - Controls
    Replies: 1
    Last Post: 01-02-2020, 02:55 PM
  3. Problem installing 3- way skylark CL dimmer
    By LISBuilder in forum Troubleshooting - Controls
    Replies: 3
    Last Post: 01-11-2018, 09:44 AM
  4. Skylark Contour C-L will NOT dim
    By dmypub in forum General Discussion - LED
    Replies: 0
    Last Post: 12-07-2017, 08:33 PM
  5. Lutron Skylark. SFSQ?LF on 115v 50Hz
    By JoeGons in forum Troubleshooting - Controls
    Replies: 5
    Last Post: 04-19-2017, 12:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •