Thread: Illumination Problem with MI Link on the last two panels out of 8

  1. #1
    Junior Member
    Join Date
    Oct 2014
    Posts
    2

    Question Illumination Problem with MI Link on the last two panels out of 8

    Hope someone can offer a few tips for checking the MI Link on a client's 15 year old HW Illumination System in a private residence that has run flawlessly up until a short while ago. Our issue is in the last two panels on an 8 panel chain. Several dimmers start to randomly flash loads on their own and all the relays start to click incessantly until the processor is rebooted which provides relief for just an hour or so. There are two H8P5 processors on the project and we swapped out the one that the 8 panels are tied to with a spare to see if that would quiet things down but the random action starts up again in less than an hour. When we run diagnostics on the system, nothing shows up on any of the links yet we know something is wrong. All the cabling runs are in conduit so we would think that this is not a case of rodents partially chewing on wires as a probable cause.This really has us stumped so we thought we would put this out there in case someone else ran into this in the past and can offer some advice on where to start looking on an MI Link.TIA.Victor
    VRM

  2. #2
    Authorized Lutron Contributor
    Join Date
    Sep 2018
    Posts
    238
    Thank you for your post vrmenigma.

    We would suggest break the RPMs down to 1 in each panel and add 1 at a time to determine if we have a bad RPM. In addition we would agree it most likely is not the MI link, as the other panels work correct? We may suggest opening up an email with hwsupport@lutron.com or giving us a call while onsite to further assist. Hope this helps!

Similar Threads

  1. DIN Panels with beakers or without.
    By krassyg in forum General Discussion - HWQS
    Replies: 1
    Last Post: 05-05-2021, 11:20 AM
  2. Dimmable T8 tubes or panels with high CRI (90 and above)
    By elwood in forum Compatibility - LED
    Replies: 1
    Last Post: 12-17-2019, 12:49 PM
  3. DIN Breaker Panels
    By BradKas in forum General Discussion - HWQS
    Replies: 0
    Last Post: 03-08-2019, 11:27 AM
  4. Multiple panels on 1 roller
    By lleo_ in forum Design Assistance - Shades
    Replies: 3
    Last Post: 05-08-2015, 03:00 PM
  5. HomeWorks panels and LED bulb control
    By Ty W. in forum Compatibility - LED
    Replies: 1
    Last Post: 07-24-2013, 12:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •