    unusual wiring to install MS-OPS2

    Hello,I want to install motion sensor switch for my basement ceiling light. I guess it's single pole.https://drive.google.com/file/d/1M3o...usp=sharingand I found that it have 2 wire (black, white) and 1 ground.I've looked at the instruction and tried all the combination of wiring but no luck.Please help, Thank you

  2. #2
    did you figure this out....i have the ms-ops2-wh with 2 black wires, a bare ground, and a white wire with green cover trying to connect to single pole with one black and one whitewhat to do with two (2 ) black wires on new switch

  3. #3
    Junior Member
    Join Date
    Mar 2021
    Posts
    2
    black wires.. one of the black wires is incoming hot (from the breaker panel) the other black wire is outgoing hot (to the device you want to control) Green/White & Green/Bare wire (or any combination of them)... these are all ground wires and MUST be tired to the ground from the breaker panel.

Similar Threads

  1. MS-OPS2 sticking o
    By Neil Gillies in forum Troubleshooting - Controls
    Replies: 7
    Last Post: 03-16-2021, 04:06 PM
  2. Ms-ops2
    By igenr8 in forum Troubleshooting - Controls
    Replies: 1
    Last Post: 09-18-2020, 01:13 PM
  3. Need help wiring MS-OPS2 dimmer
    By Don Van O in forum Troubleshooting - Controls
    Replies: 1
    Last Post: 05-01-2020, 03:19 PM
  4. Replies: 2
    Last Post: 02-27-2019, 11:36 AM
  5. three MS-OPS2 in parallel
    By pauloeuvray@hotmail.com in forum Design Assistance - Controls
    Replies: 1
    Last Post: 02-27-2017, 11:47 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •