    Pd-6wcl 3way

    I followed the video but I'm still having issues. I took switch A and placed all 3 wires together. Switch B has the common going to the caseta wireless, and has the other two wires going to the other caseta wireless wire. However after turning the power back on the lights just stay on and no leds on the caseta. I took a wire off of the caseta and the lights still came on after reset. Can I not place the caseta on these wires? I really don't want it on the other switch spot.

    Thanks for any help.
    Neil

  2. #2
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    635
    Quote Originally Posted by Neilalp View Post
    I followed the video but I'm still having issues. I took switch A and placed all 3 wires together. Switch B has the common going to the caseta wireless, and has the other two wires going to the other caseta wireless wire. However after turning the power back on the lights just stay on and no leds on the caseta. I took a wire off of the caseta and the lights still came on after reset. Can I not place the caseta on these wires? I really don't want it on the other switch spot.

    Thanks for any help.
    Neil
    Neil, it sounds like you wired it correctly, but something seems to be a little unusual with your 3-way wiring. Could you please call our 24-hour Technical Support hotline at 1-844-588-7661? We should be able to help you wire this up and get this running within 1/2-hour at most.

    Brian

  3. #3
    Junior Member
    Join Date
    Nov 2015
    Posts
    4
    Quote Originally Posted by Brian W. View Post
    Neil, it sounds like you wired it correctly, but something seems to be a little unusual with your 3-way wiring. Could you please call our 24-hour Technical Support hotline at 1-844-588-7661? We should be able to help you wire this up and get this running within 1/2-hour at most.

    Brian
    Neil, were they able to help you? I have the same issue. May be calling that phone # tomorrow.

    Cheers,

    Eric

  4. #4
    Junior Member
    Join Date
    Nov 2015
    Posts
    4
    Quote Originally Posted by EricV View Post
    Neil, were they able to help you? I have the same issue. May be calling that phone # tomorrow.

    Cheers,

    Eric
    Customer support got me sorted out right away. Turns out wiring in the Chicago area is different and in a three way, the hot wire is the odd colored one. The key was to connect the two same colored wires to one of the black Caseta wires and the odd-colored wire to the other black wire.

Similar Threads

  1. PD-6WCL in a 3-Way Setup
    By Kevin P. in forum Design Assistance - CAS
    Replies: 1
    Last Post: 10-29-2020, 08:21 PM
  2. In-wall light dimmer (PD-6WCL) - only 80% maximum brightness?
    By nester in forum Troubleshooting - CAS
    Replies: 1
    Last Post: 07-31-2017, 07:26 PM
  3. Cannot Reset Caseta Dimmer PD-6WCL
    By MFSchar in forum Troubleshooting - CAS
    Replies: 3
    Last Post: 07-20-2015, 08:06 PM
  4. Lutron PD-6WCL-WH In Wall Dimmer compatibility with outlet
    By Jaybrones in forum General Discussion - CAS
    Replies: 1
    Last Post: 02-09-2015, 11:29 AM
  5. 3way 4way 3way dimming leds
    By greenjourneyman in forum General Discussion - LED
    Replies: 2
    Last Post: 11-07-2013, 05:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •