Thread: Bath Fan & PD-6WCL

  1. #1
    Junior Member
    Join Date
    Dec 2019
    Posts
    5

    Bath Fan & PD-6WCL

    I am looking to automate the bathroom a bit by putting in a temperature and humidity sensor and would like to turn on the fan when a certain humidity level is reached and shutoff when it has lowered enough. Will the PD-6WCL function just fine as a on/off for the bath fan? Thanks! #Edit# Fan is a simple 1 speed fan, no speed control necessary for it.

  2. #2
    Junior Member
    Join Date
    Dec 2019
    Posts
    5
    Looks like I should just use the PD-6ANS.

  3. #3
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    2DruKe- you are correct. Running a dimmer for an exhaust fan will burn up the motor and/or the dimmer. Use the 6ANS
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

Similar Threads

  1. PD-6WCL in a 3-Way Setup
    By Kevin P. in forum Design Assistance - CAS
    Replies: 1
    Last Post: 10-29-2020, 08:21 PM
  2. Pd-6wcl-wh
    By heatman5 in forum General Discussion - RA2
    Replies: 2
    Last Post: 09-19-2019, 10:31 PM
  3. what's the difference PD-6WCL-WH vs PD-6WCL-WH-R
    By floridaboy in forum General Discussion - Controls
    Replies: 2
    Last Post: 05-14-2019, 04:44 PM
  4. Bath Fan Won't Work if Light Dimmer Set High
    By kmayer in forum Troubleshooting - Controls
    Replies: 2
    Last Post: 11-27-2018, 02:32 PM
  5. Flaky PD-6WCL ?
    By hgmobile in forum Troubleshooting - CAS
    Replies: 0
    Last Post: 10-18-2017, 05:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •