Thread: Partial System on Generator

  1. #1
    Senior Member
    Join Date
    Oct 2013
    Posts
    247

    Partial System on Generator

    Remodel will have ra2 in new areas and old. Client wants backup gen panel to control emergency loads and lights/keypad in kitchen. Main Rep will be on backup gen but possible aux rep will not. What would be the problems, if any, if only the main rep and kitchen have power. I'm not concerned about the lights in other areas that have no power. More wondering about communication loss because of the aux not having power.

  2. #2
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    Won't have any issues. 10 non-volatile memory. May have issues with LED logic upon reinstatement of power, but it will sort itself out once the homeowner starts pushing buttons again or timeclocks fire. Just keep the main close to the area on back-up.
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

Similar Threads

  1. Transfer with partial activation?
    By fx12002 in forum Troubleshooting - RA2
    Replies: 1
    Last Post: 11-08-2019, 09:52 PM
  2. Generator Emergency on lights on the RPM cycle on then off
    By Jeffht in forum Troubleshooting - HWQS
    Replies: 1
    Last Post: 09-17-2019, 04:51 PM
  3. Suggestions on how to integrate a split-system ductless HVAC system with RadioRA2
    By RA2-Designer-Gal in forum Design Assistance - RA2
    Replies: 4
    Last Post: 05-10-2017, 11:43 AM
  4. Generator load-shedding scheme
    By scopp in forum Programming - HWQS
    Replies: 11
    Last Post: 06-23-2014, 09:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •