Thread: Wiring Temporary Construction Lighting

  1. #1

    Wiring Temporary Construction Lighting

    We are currently roughing in a homeworks system and the builder would like to have temporary lighting up throughout construction. We have done this before but im thinking it wasnt in the most efficient way. I am wondering other ways to go about this with out installing modules and programming.

  2. #2
    Senior Member
    Join Date
    Oct 2013
    Posts
    1,514
    Quote Originally Posted by ChandlerHart View Post
    We are currently roughing in a homeworks system and the builder would like to have temporary lighting up throughout construction. We have done this before but im thinking it wasnt in the most efficient way. I am wondering other ways to go about this with out installing modules and programming.
    With RPMs you can land the wires in the RPM panel and use the breakers to turn the lights on/off. You can also use the manual override on the module interface (requires RPMs to be installed). DIN modules have a manual override CCI.

    This is getting to be a routine request. If the electrical system is ready for temp lighting, the Lutron system should be as well. I typically only do 1 or 2 keypads and only give them an interior on/off and exterior on/off. Some are now asking for exterior timers to keep some of the lights on overnight.
    LED, Incorporated
    Raleigh, NC 27614

  3. #3
    Junior Member
    Join Date
    Mar 2020
    Posts
    1
    DIN modules have a manual override CCI.
    Download Mod Skin Lol 2020, and enjoy all premium skin for free

  4. #4
    Senior Member
    Join Date
    Oct 2013
    Posts
    1,514
    Quote Originally Posted by deepakwon View Post
    DIN modules have a manual override CCI.
    "Input is Normally Closed. If Contact Closure is opened, the unit will go to Emergency light levels or Manual Override light levels and will not respond to inputs from other devices (LQSE modules only)."
    LED, Incorporated
    Raleigh, NC 27614

Similar Threads

  1. New construction
    By joeyb8099 in forum General Discussion - CAS
    Replies: 4
    Last Post: 12-28-2019, 12:46 AM
  2. Best 6” New Construction Cans?
    By schalliol in forum General Discussion - RA2
    Replies: 6
    Last Post: 09-18-2018, 12:47 AM
  3. New Construction, Wiring, LED housing
    By tech1 in forum General Discussion - RA2
    Replies: 0
    Last Post: 09-18-2018, 12:42 AM
  4. Best design for new construction
    By Jmelani in forum Design Assistance - RA2
    Replies: 2
    Last Post: 05-15-2014, 01:10 AM
  5. Temporary lighting for construction
    By BradKas in forum General Discussion - HWQS
    Replies: 4
    Last Post: 12-09-2013, 09:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •