Thread: Help needed! 1000 Watts LEDs on RRD-10ND - do I need a PHPM-PA?

  1. #1

    Exclamation Help needed! 1000 Watts LEDs on RRD-10ND - do I need a PHPM-PA?

    Help needed!

    So I have a client has decided to go LEDs due to the high wattage Incandescent issue in his installation - 2400 watts on one circuit.

    So we spec'd out an LED candelabra bulb that will work at 25 Watts and is listed to work with the10ND.

    However, I am uncertain that the 1000 watts of LEDs will work on the 10ND. The new bulbs comes out to be exact 1000 watts -
    8 bulbs per fixturex25 watts=200 200 watts x 5 fixtures=1,000 watts

    And I seem to recall that the LEDs draw a lot more power when ramping on. My instincts are telling me to add in the PHPM-PA anyways due to the ramp on issue.

    However, it seems towork fine in the RA2 software - no caution signs pop up.

    And the electrician has agreed to install the 10ND in its own box so no deganging issues there.

    But I still have a nagging feeling the PHPM-PA is still needed.


    Thank you in advanace - I so appreciate your feedback & suggestions!

  2. #2
    You mean equivalent to a 25w incandescent light output? But how much power do they actually use? 6w? Usually it is a factor of 4 derating meaning 250w of leds or 41 6w bulbs.

  3. Thanks RA2-Designer-Gal thanked for this post
  4. #3
    Ughhhh! Blond moments are so embarassing. Thank you!

    Yes - it would be 3.8 watts instead so 160 total. So I should be fine.

    Toshiba bulb 4B11/27CF-UP
    8bulbs x4 watts=32 32x5 fixtures=160

  5. #4
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    RA2-Designer-Gal, see the LED Product Selection Tool at www.lutron.com/led. The specific page for the lamps you are using is here: http://www.lutron.com/en-us/Resource...JUN%20RevA.pdf

    Max number of these lamps per Lutron's testing is 39 on a 10ND, power module isn't listed as compatible with these bulbs. You can call the LED hotline at 877-DIM-LED8 and see if they have some updated numbers.
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

  6. Thanks RA2-Designer-Gal thanked for this post
    Likes RA2-Designer-Gal, Armando B. liked this post
  7. #5
    Seems weird that the older 6ND support 57 but the newer 6ND only support 39 and the 10ND doesn't support any additional.

  8. #6
    Authorized Lutron Contributor
    Join Date
    May 2013
    Posts
    513
    When we tested this application, the numbers represent a consistent and steady dimming to the best performance possible with the specific dimmers selected.

  9. #7
    Thanks for the clarification. Still surprising that there is such a big difference in the 'best performance maximum' between a hwd-6nd and a rrd-6nd.

Similar Threads

  1. Can I put to PHPM-PA-120-WH on to a RRD-10D dimmer?
    By RA2-Designer-Gal in forum Design Assistance - RA2
    Replies: 6
    Last Post: 03-23-2017, 04:41 PM
  2. QS + DMX Lighting Design Help Needed
    By jkvossen in forum Design Assistance - HWQS
    Replies: 4
    Last Post: 09-09-2014, 04:14 PM
  3. QS parts needed
    By sdaven in forum General Discussion - HWQS
    Replies: 2
    Last Post: 02-03-2014, 08:51 PM
  4. how many Incandescent watts dimmable
    By greenjourneyman in forum Design Assistance - Controls
    Replies: 1
    Last Post: 11-13-2013, 09:29 PM
  5. HQRD-10ND Dimmer Getting Very Hot
    By jwanderson in forum Troubleshooting - HWQS
    Replies: 1
    Last Post: 10-23-2013, 10:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •