Thread: Pro switch MLV blow off before i'm able to change ELV Mode

  1. #1
    Junior Member
    Join Date
    Aug 2019
    Posts
    2

    Pro switch MLV blow off before i'm able to change ELV Mode

    Hello, i bought a pro dimmer to work with my MLV recessed light. I followed the instruction ad the wiring is perfect. But by the time i put the breaker to ON and i get to the dimer to change the default mode from ELV to MLV the dimmer blow. In the instruction it tell to not power on the dimmer without load but it's the only way i think to change the mode before having a load and blow it again. Do you see any problem to power the dimmer without load change the mode and after plug the load??

  2. #2
    Lutron Technical Support
    Join Date
    May 2013
    Posts
    635
    I would recommend that before you turn the breaker on, pull the FASS tab out to cut power at the dimmer, then turn the breaker on. With the FASS tab pulled out, the dimmer and load won't be powered up from the breaker until you push the FASS tab pushed back in.When you get back the dimmer, follow the directions here to change the phase: https://www.casetawireless.com/docum...ange-phase.pdf.

  3. #3
    Senior Member
    Join Date
    Oct 2013
    Posts
    2,587
    If you have the hot and neutral connected but not the load, the dimmer should power up. If it doesn't, it's broken.

    Some documents say the neutral is optional or not required. Life will be much easier if you use the neutral.
    Convergence Technologies Raleigh, North Carolina
    www.convergenceusa.com

  4. #4
    Junior Member
    Join Date
    Aug 2019
    Posts
    2
    I have a neutral, do you see any problem to power it with hot and neutral only and no load? In the instruction they say to not power up the dimmer without load.

  5. #5
    Senior Member
    Join Date
    Jun 2013
    Posts
    1,365
    We power up neutral dimmers all the time without a load. Happens more than you would think in new construction or big remodels. Designer hasn't selected the chandelier by programming day. Power the dimmer, and we activate and transfer all the time in RA2. In your case, turn off the breaker and disconnect the load. Pull the FASS switch, go turn on the breaker, and come back. Close the FASS switch, perform the mode change. Close FASS, turn off breaker, attach load, turn on breaker, and close FASS. These things are pretty solid, hard to "blow up". I've tried.
    Simple automation when DIY isn't working
    intuitivehomecontrols@gmail.com
    fb.me/intuitivehomecontrols

Similar Threads

  1. Away mode (vacation mode)
    By dougpark464 in forum General Discussion - RA2
    Replies: 4
    Last Post: 10-12-2017, 12:01 PM
  2. Feature Request - enable VCRX to change Timeclock mode
    By freeoscar in forum Programming - RA2
    Replies: 0
    Last Post: 08-18-2017, 11:23 AM
  3. Away change thermostats to 61F how to change that
    By donmor in forum Troubleshooting - RA2
    Replies: 3
    Last Post: 01-07-2017, 08:25 PM
  4. Change hold action on dimmer switch
    By KDMBUILDERS in forum Programming - HWQS
    Replies: 1
    Last Post: 10-25-2016, 09:42 AM
  5. Replies: 3
    Last Post: 01-13-2014, 07:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •