Also, this was the smallest load and maybe the shortest run.
Also, this was the smallest load and maybe the shortest run.
The RA2 software has that spiffy tool for testing low end trim settings. Nothing for testing high-end trim. Hmm....
Convergence Technologies Raleigh, North Carolina
www.convergenceusa.com
Hmm........
MitcheE, did the smallest run have its own driver? ELV or MAG? Also, if Mag in particular.... was it over 80 percent load of the driver? I have seen this when you don't use enough of the load of the driver it will act irrationally. So like if you have a 40 watt magnetic transformer and only use 10 watts of led on it...